Results 1 to 28 of 28
  1. #1
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default What do you think

    Haven't seen this before. Does the diameter of this pipe make it acceptable to vent properly.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: What do you think

    Not likely to cause a problem, but should have (required to have) an AAV.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    Mar 2007
    Location
    Baton Rouge, La.
    Posts
    91

    Default Re: What do you think

    See it often at island sinks. No known problems but I still explane the loop system for island drains.

    James

    James Bohac

  4. #4
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: What do you think

    That looks like remodeling work.
    Did you look at the other vents? Bath, toilet

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  5. #5
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: What do you think

    Scratch my last post, looks like it is a Bar sink.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  6. #6
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: What do you think

    I think original equipment but who knows. thanks for the quick replies


  7. #7
    Join Date
    Mar 2007
    Location
    Oklahoma City
    Posts
    357

    Default Re: What do you think

    They allow it here as long as the pipe is at least 1.5 x larger.

    If it weren't for lawyers, we would never need them.

  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: What do you think

    Quote Originally Posted by wayne soper View Post
    Haven't seen this before. Does the diameter of this pipe make it acceptable to vent properly.

    Not following what you are asking, but, yes, it is acceptable to vent it properly ... (which it is not)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Mar 2007
    Location
    Ft. Myers, FL
    Posts
    363

    Default Re: What do you think

    Quote Originally Posted by wayne soper View Post
    Haven't seen this before. Does the diameter of this pipe make it acceptable to vent properly.
    They still make TANG?

    Paul Kondzich
    Ft. Myers, FL.

  10. #10
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    4

    Default Re: What do you think

    Maybe it was an astronauts house.


  11. #11
    Join Date
    Mar 2007
    Location
    Kalamazoo, MI
    Posts
    117

    Default Re: What do you think

    Doesn't look like an AAV on the top of the pipe??? If not, needs an AAV I believe.

    RJDalga
    http://homeanalysts.com
    Kalamazoo, MI

  12. #12
    Joshua Hardesty's Avatar
    Joshua Hardesty Guest

    Default Re: What do you think

    James: What loop?

    Frank: 1.5x larger? So, in your area a 2" shower drain needs to be vented by a 3" pipe?

    Robert: It's not a vent, it's a rubber cap. So...

    That's an elaborate S-trap. Plumber probably didn't have one on the truck at the time, forgot to go back and put one on. Or was lazy.


  13. #13
    Join Date
    Mar 2007
    Location
    Kalamazoo, MI
    Posts
    117

    Default Re: What do you think

    That's not an S-Trap and if that's a rubber cap the plumber forgot the AAV.

    RJDalga
    http://homeanalysts.com
    Kalamazoo, MI

  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: What do you think

    Quote Originally Posted by Robert Dalga View Post
    That's not an S-Trap and if that's a rubber cap the plumber forgot the AAV.

    Because they did not vent it, it is effectively an S-trap ... it will suffer from the same problems for the same reasons.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: What do you think

    Quote Originally Posted by Jerry Peck View Post
    Because they did not vent it, it is effectively an S-trap ... it will suffer from the same problems for the same reasons.
    An S-trap could siphon itself dry, and that is a bad thing. Are you saying this unvented P-trap will siphon itself dry? I think not.

    No offence intended, I know it is not correctly plumbed. But I suspect it works just fine. There is no way there will be enough suction on that trap to draw water out of it. I would point it out as incorrect and move on.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  16. #16
    Join Date
    Mar 2007
    Location
    Oklahoma City
    Posts
    357

    Default Re: What do you think

    They do them that way under peninsula and island kitchen cabinets here all the time and they work fine. The AHJs here do allow it and it is commonplace on new construction.

    I know, only in OK and we're a bunch of morons, blah blah blah.

    If it weren't for lawyers, we would never need them.

  17. #17
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: What do you think

    Quote Originally Posted by John Kogel View Post
    An S-trap could siphon itself dry, and that is a bad thing. Are you saying this unvented P-trap will siphon itself dry? I think not.
    You can bet it will, in fact ... that is why it is required to be vented.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  18. #18
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: What do you think

    Quote Originally Posted by Frank Bombardiere View Post
    They do them that way under peninsula and island kitchen cabinets here all the time and they work fine. The AHJs here do allow it and it is commonplace on new construction.

    That is not how island and peninsula sinks are done ... at least that is not how they are SUPPOSED to be done ...

    If they are being done that way then they are wrong.

    I suspect, however, that you are only thinking they are "done that way" when in reality they are done properly and you are just not noticing the difference.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  19. #19
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: What do you think

    A AAV will not work unless its installed above the flood rim.

    Attachment of an island sink venting set up.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  20. #20
    Ron Bibler's Avatar
    Ron Bibler Guest

    Default Re: What do you think

    Quote Originally Posted by Raymond Wand View Post
    A AAV will not work unless its installed above the flood rim.

    Attachment of an island sink venting set up.
    I like what Raymond has posted. this is what I put on my reports.

    Best

    Ron Bibler
    EXCELLENCE HOME/BUILDING INSPECTION SERVICE
    Petaluma California Home Inspection - Exterminating & Thermal Imaging
    www.sonomahomeinspection.com
    Vacaville California Home Inspection - Exterminating & Thermal Imaging


  21. #21
    James Duffin's Avatar
    James Duffin Guest

    Default Re: What do you think

    Quote Originally Posted by wayne soper View Post
    Haven't seen this before. Does the diameter of this pipe make it acceptable to vent properly.

    It looks ok as long as the 3" trap arm is not over 12 feet.


  22. #22
    James Duffin's Avatar
    James Duffin Guest

    Default Re: What do you think

    Quote Originally Posted by Raymond Wand View Post
    A AAV will not work unless its installed above the flood rim.

    Attachment of an island sink venting set up.
    Here is what the NC code says about the location of AAV's. Your state's code may be different when it comes to the required height.



    917.4 Location. The air admittance valve shall be located a
    minimum of 4 inches (102 mm) above the horizontal branch
    drain or fixture drain being vented The air admittance valve
    shall be located within the maximum developed length permitted
    for the vent. The air admittance valve shall be installed a
    minimum of 6 inches (152 mm) above insulation materials.



  23. #23
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: What do you think

    Quote Originally Posted by Jerry Peck View Post
    You can bet it will, in fact ... that is why it is required to be vented.
    Jerry, I believe the rule says it will but I say it won"t.
    I challenge you to make a 3" plumbing stack draw hard enough on a 1" P-trap to suck a teaspoon of water.

    It is 9 times larger in volume.

    Last edited by John Kogel; 05-03-2010 at 07:32 PM. Reason: rude
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  24. #24
    Jon Kauffman's Avatar
    Jon Kauffman Guest

    Default Re: What do you think

    If it's less than 12' to a vent, wouldn't it be considered a wet vent which would be acceptable?


  25. #25
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: What do you think

    Quote Originally Posted by Raymond Wand View Post
    A AAV will not work unless its installed above the flood rim.

    An AAV *does not* need to be above the flood level rim of the fixture.

    Not sure where you got that information from?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  26. #26
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: What do you think

    Quote Originally Posted by Jerry Peck View Post
    An AAV *does not* need to be above the flood level rim of the fixture.

    Not sure where you got that information from?
    Jerry

    I am glad you asked the question.

    the Ontario Building Code, Section 7.5.9.2 ("Air Admittance Valves") states that "The air admittance valves shall be located, (a) above the flood level rim of the fixture it serves, ..."

    This definition is provided:

    Flood level rim means the top edge at which water can overflow from a fixture or device.


    7.5.9.2. Air Admittance Valves
    (1) Air admittance valves shall only be used to vent,
    (a) fixtures in buildings undergoing renovation, and
    (b) installations where connection to a vent may not be practical.
    (2) The air admittance valves shall be located,
    (a) above the flood level rim of the fixture it serves,
    (b) within the maximum developed length permitted for the vent,
    (c) not less than 150 mm above insulation materials, and
    (d) installed in a location not subject to back pressure.
    (3) Air admittance valves shall,
    (a) only vent fixtures located on the same storey, and
    (b) be connected to the horizontal fixture drain.

    7.5.9.3. Installation Conditions
    (1) Air admittance valves shall not be installed in supply or return air plenums, or in locations where they may be exposed to freezing temperatures.
    (2) Air admittance valves shall be installed in accordance with the manufacturer’s installation instructions.
    (3) Air admittance valves shall be rated for the size of vent pipe to which they are connected.
    (4) Installed air admittance valves shall be,
    (a) accessible, and
    (b) located in a space that allows air to enter the valve.
    (5) Every drainage system shall have one vent that terminates to open air in conformance with Sentence 7.5.6.2.(1).


  27. #27
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: What do you think

    Quote Originally Posted by Raymond Wand View Post
    the Ontario Building Code, Section 7.5.9.2 ("Air Admittance Valves") states that "The air admittance valves shall be located, (a) above the flood level rim of the fixture it serves, ..."

    Not required by any AAV manufacturer, but ... if Ontario decides it knows better than everyone else, so be it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  28. #28
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: What do you think

    Good morning Jerry,

    I did note the caveat in the code reference about manufactures instructions.

    Thanks for the feedback.

    Cheers,


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •