    I inspected a house today that had a Majestic MIM2436 Fireplace Insert installed. The best I call tell this has to be installed in a masonary fireplace but this one was installed like a zero clearance fireplace with a triple wall flue. I looked on the Majestic web site for the manual and it was not available.

    My question is "Is there any way this insert can be installed without being in a masonary fireplace?" I don't think so but wanted to see if anyone had access to a manual.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: Majestic MIM2436 Fireplace Insert

    That missing manual will be the key to the answer. Until that's found all you can do is raise a question about the installation. From your photos I'm going to guess that the fireplace is an older unit. Manufactured fireplaces have limitations on their expected lives and that one just might be going into borrowed time anyway.

    Eric Barker, ACI
    Lake Barrington, IL

  3. #3
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Majestic MIM2436 Fireplace Insert

    .
    Try Majestic Products - Customer Care Brochures, Manuals and Specification Sheets

    Or Contact Customer Service
    .
    Or Check Your Model #
    * I'm not seeing it.
    .

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  4. #4
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Majestic MIM2436 Fireplace Insert

    I didn't see it either but thanks for looking. I swear it looks like they installed a fireplace insert without a fireplace.


  5. #5
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Majestic MIM2436 Fireplace Insert

    Quote Originally Posted by James Duffin View Post
    I inspected a house today that had a Majestic MIM2436 Fireplace Insert installed. The best I call tell this has to be installed in a masonary fireplace but this one was installed like a zero clearance fireplace with a triple wall flue. I looked on the Majestic web site for the manual and it was not available.

    My question is "Is there any way this insert can be installed without being in a masonary fireplace?" I don't thin
    k so but wanted to see if anyone had access to a manual.
    Quote Originally Posted by James Duffin View Post
    I swear it looks like they installed a fireplace insert without a fireplace.
    .
    .
    It's Called A Chase Installed Factory Built Fireplace.
    .
    .

    Attached Files Attached Files
    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  6. #6
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Majestic MIM2436 Fireplace Insert

    The data plate on the insert calls for a 12" clearance from combustible on both sides and this installation has zero clearance. I have not seen a chase installed fireplace that requires a 12" clearance so I am looking for input from folks that have.


  7. #7
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: Majestic MIM2436 Fireplace Insert

    What does the rating plate say it is listed to: UL127, which would make it a factory built fireplace or UL 1482, which would make it a woodstove?

    Please, everyone, eradicate that term "zero clearance" from your vocabulary. It has led to many homes burning down because people assume the entire fireplace and chimney must be zero clearance, which they are not; Only to the floor.

    You cannot install woodstove inserts into factory built fireplaces-period. They would all have to be tested and listed as a system: fireplace, stove and liner and to date not one mfr. has figured out how to do this. It is a fire hazard.

    James, this is a good pickup but all you need to do now is call for the Level II and move on.

    Keep the fire in the fireplace.

  8. #8
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Majestic MIM2436 Fireplace Insert

    Thanks Bob. I'll try to get back into the house and take a look at the UL listing. I was hoping you would chime in!


  9. #9
    Join Date
    Jul 2009
    Location
    Virginia Beach
    Posts
    25

    Default Re: Majestic MIM2436 Fireplace Insert

    I'd be careful about calling this installation wrong without seeing the manual for the insert and fireplace. The chimney pipe is clearly old Majestic pipe and if you know the insert is made by Majestic this may be one of the few (rare) times when the insert is properly listed and approved for the fireplace.


  10. #10
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Majestic MIM2436 Fireplace Insert

    I agree Jim. Based on the information available on the data tag the unit is only approved for installation in a masonry fireplace and there is no fireplace in this house.....only the insert installed in a wood chase. I find it hard to believe that someone would have installed this insert the way they did if the manual did not say it was okay. But I have no way to be sure so I called for further evaluation by a fireplace specialist.


  11. #11
    Rick Fifield's Avatar
    Rick Fifield Guest

    Default Re: Majestic MIM2436 Fireplace Insert

    I think that is the best call.


  12. #12
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Majestic MIM2436 Fireplace Insert

    Update:

    The buyer finally found a fireplace company that knew about this type of installation. Come to find out there was a prefab fireplace hidden by the wood stove. The installer had removed all of the refectory material inside the firebox to make the wood stove fit. This had done away with the zero clearance rating of the fireplace plus the installation had several other problems. The buyer got a $4500 allowance to replace the fireplace. The bank made the seller drywall over the fireplace before they would close on the house.

    As a side note the seller had been in the house about six years and had the house inspected when he bought it. He was not a happy camper that he had to do over $8000 in repairs that were missed by his inspector. He was curious as to what liability a HI has when he misses EVERYTHING! I told him to call the inspector and talk to him. Hope it all works out for the inspector! I did not bad-mouth the inspector at all to the seller as to give him a fighting chance to get it worked out.


  13. #13
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Question listing reference for woodstove into factory built Fp

    Quote Originally Posted by Jim Brewer View Post
    I'd be careful about calling this installation wrong without seeing the manual for the insert and fireplace. The chimney pipe is clearly old Majestic pipe and if you know the insert is made by Majestic this may be one of the few (rare) times when the insert is properly listed and approved for the fireplace.
    Jim, can you provide exactly which standard Majestic was able to "properly" list an insert woodstove into a UL 127 factory built fireplace and when? Please provide model and production run dates if possible.
    Thanks in advance,
    Bob

    Keep the fire in the fireplace.