Thread: Panel setup
05-13-2010, 07:20 PM #1
Panel setup
Question answered. Thanks.
Similar Threads:Last edited by Jody Humbert; 05-13-2010 at 07:27 PM.
05-13-2010, 07:28 PM #2
Re: Panel setup
The breaker above which I highlighted in red is "backfed". That breaker needs to be secured in place with a proper bracket, clip, screw, etc., as per the manufacturer's designs so that the breaker cannot simply be pulled off the bus bar - it is fed from its terminals, which will be 'hot' and exposed when the breaker is removed from the bus bar.
Yeah, the wiring of that setup is kinda screwy all right, basically wastes two panels and still only has a 100 amp service.
Correct. The panel downstream is not the service equipment, it is simply a panel.The panel downstream should have its neutrals and grounds separated.
Someone had no idea of what they were doing or the correct way to do it?Why are these panels installed like this?
05-13-2010, 07:50 PM #3
Re: Panel setup
I hate it when people feel the need to delete their original post and photos. This is a forum for all of us to learn from. Jody has learned and prevented the rest of us from benefiting. I will try to remember to not respond to any of Jody's posts.
05-13-2010, 08:47 PM #4
Re: Panel setup
Gunnar. I thought I had deleted the information before anyone seen the post. I had a local electrician who I question and answer with on occasion call me as I was posting and he kinda spelled it out for me. I do appreciate any and all info that is shared on this forum. I learn more everyday when I log onto this forum. Thanks Jerry for your reply. You pointed out more than we discussed. I apologize for any misconceptions.
05-14-2010, 06:01 PM #5
Re: Panel setup
Jody,
Now that you posted photos ... you have some BIG PROBLEMS in those panels, to start with ... there is no neutral to the panel in the second photo, just a bare ground going "someplace", and no raceway for the conductors coming in from the bottom left, and ... man, it just gets bad ...