Results 1 to 2 of 2
  1. #1
    Jon mackay's Avatar
    Jon mackay Guest

    Default Ground rod in slab

    1960s construction.

    The ground cable from the service panel enters the slab a couple inches away from a grounding rod. I can not verify that the cable is actually attached to the rod.
    I entered the ground as not inspected but was curious what others might say in addition to this.
    Would you recommend a new ground to ensure that there actually is a proper connection?

    In the photo, the black cable is for other equipment.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Ground rod in slab

    A couple of quick observations:
    - that is a pipe clamp, not a rod clamp
    - the ground rod is (presumable) 8 feet long and is quite obviously therefore not 8 feet in the ground
    - that black ground conductor to "other equipment" is likely all wrong

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •