    Default Corrosion/Deposit at Trane Furnace

    Any opinions/ information on the significance (or lack of same) of the corrosion/deposits at this furnace?

    Thanks

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  2. #2
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: Corrosion/Deposit at Trane Furnace

    Looks like 99% of the ones I've seen lately. Condensation leaks, Service and monitor.


  3. #3
    Join Date
    Mar 2007
    Location
    Succasunna NJ
    Posts
    577

    Default Re: Corrosion/Deposit at Trane Furnace

    It looks like a drainage problem. I've seen quite a few of those little rubber drain hoses 'pinched' so the condensation doesn't drain.

    Darren www.aboutthehouseinspections.com
    'Whizzing & pasting & pooting through the day (Ronnie helping Kenny helping burn his poots away!) (FZ)

  4. #4
    Join Date
    May 2007
    Location
    Frankfort, KY
    Posts
    326

    Default Re: Corrosion/Deposit at Trane Furnace

    That unit is also not installed according to manufacturers installation instructions.

    Any 120,000 BTU furnace is supposed to have a return drop pulled from both sides or from the bottom but not one side only.