    Default Is a bare neutral ok here?
    Service panel, 1989 home. Looks like metal conduit from meter can on the left. At the weatherhead, the neutral was insulated, so there's a splice at the meter?
    Default Re: Is a bare neutral ok here?
    The neutral coming out the top of the weatherhead is typically insulated, it ties to the neutral/ground from the overhead service drop conductors, it then lands on the neutral/ground connection at the meter, grounding the meter can.
    From there, the neutral/ground can run to the service equipment as either bare or insulated, so ...
    Given the above scenario, yes, the neutral/ground is allowed to be bare to the service equipment.
    Thanks, Jerry. I have another question coming shortly.
    Oct 2009
    michigan
    Regarding the bare/insulated splice: service conductors can be spliced w/certain conditions but not within a raceway w/o an accessible cover.
    Funny how code allows the grounded/neutral conductor to be run thru a metallic raceway without bonding both ends, yet the GEC cannot.
    Under a major fault, that grounded conductor would carry many more amps than say, a GEC to a few earthing rods. Just a rambling thought.
    Bob Smit, County EI