    Default Country Inspector Wrong?

    New construction - approved by the county.

    3 wire feed to service panel. Neutral and ground buses are NOT bonded to one another inside the panel. I suspect they are at the rebar bond just below the panel as there is one copper ground from the neutral bus and one from the ground bus leaving the bottom of the panel.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Country Inspector Wrong?

    Quote Originally Posted by Matt Fellman View Post
    Neutral and ground buses are NOT bonded to one another inside the panel.
    Yes they are.

    See that green bonding screw below and to the left of the main? That is bonding the neutral terminal bars to the enclosure, which is where the grounds are bonded to. That means the grounds are bonded to the neutrals through that green screw.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Oregon
    Posts
    2,365

    Default Re: Country Inspector Wrong?

    Thanks JP.... I was pretty sure that's what that was for.