    Default Condensate trapping for Fedders wall-mount electric furnace

    Anyone have the documentation for this unit?

    CFE018CFC

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  2. #2
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Condensate trapping for Fedders wall-mount electric furnace

    Well, son of a gun.

    Fedders gave me that name of of a guy who knows everything there is to know about these units, and who faxed me the original installation instructions ("Al" at RSI Inc, 800-221-1000 on the very slim chance that someone will subsequently find this thread via a search .."I don't believe I've open that file cabinet for 20 years".

    And darned if they don't specify a P trap on that condensate line - as well as a secondary drain pan when installed "over an occupied area".

    So we we now know that at least as early as 1974 (the date of this unit's manufacture), at least some manufacturers already required trapping of the condensate line.