Results 1 to 13 of 13
    Jul 2007
    Default Control/expansion joint brick veneer over frame
    Developer called me crazy for recommending a control joint on a two story SFR with multiple fenestrations, single wythe veneer wall approx 55' wide and 22' high. I merely posted this in front of him: Masonry Magazine: Control Joints
    So the Developer did not install and the property closed. Who's right? BIA states the same thing here: http://www.gobrick.com/BIA/technotes/t18a.pdf?CFID=10894316&CFTOKEN=28364765
    Default Re: Control/expansion joint brick veneer over frame
    Quote Originally Posted by Ross Neag View Post
    Fenestrations? Sheesh.
    Mark Howe's Avatar
    Mark Howe Guest
    Is the wall a CMU veneer or a brick veneer wall? The magazine article is concerned with 'control' joints. Control joints are typically associated with concrete masonry. When talking about brick veneer, the primary joint used is an ''expansion' joint. The terms are not interchangeable.
    If I built a brick veneer wall and you gave me an article on CMU control joints, I might think you were crazy, too (I kid).
    As far as who is right, I would have to know the masons argument and see some pictures before I could hazard a guess.
    Jul 2007
    Vertical Expansion Joints. A vertical expansion joint consists
    of an opening through the brick wythe closed with a
    backer rod and sealant. A compressible pad may be used
    in the joint to ensure no mortar is placed in the expansion
    joint. Such pads can be made of premolded foam or neoprene
    as shown in Figure 11. Vertical expansion joints should
    extend from the foundation to the top of the brickwork without
    deviating from vertical. When this is not possible, they can
    be terminated at horizontal expansion joints. Generally, the
    spacing of vertical expansion joints should not exceed 30 ft
    (9.14 m) in walls without openings. Vertical expansion joints
    are also recommended where site walls adjoin buildings and
    at the corners of large openings. Building corners should
    have a vertical expansion joint located within 10 ft (3.05 m) of
    the corner. When a vertical expansion joint is located within
    10 ft (3.05 m) of the corner, the vertical expansion joint on the other wall forming that corner should be placed at
    the typical spacing between expansion joints. For example, if the spacing between vertical expansion joints on a
    straight wall is 25 ft (7.62 m), then the spacing of expansion joints around a corner could be 10 ft (3.05 m) on one
    side of the corner and 15 ft (4.57 m) on the other side. Plan offsets and setbacks of a wall should also include a
    Go here: Technical Notes
    Click on the link on the left to Technical Notes 18A.
    This may (should) take you directly there: http://www.gobrick.com/BIA/technotes/t18a.pdf
    chris mcintyre's Avatar
    chris mcintyre Guest
    So the Developer did not install and the property closed. Who's right? BIA states the same thing here: http://www.gobrick.com/BIA/technotes...TOKEN=28364765
    I never see expansion joints used in SFR, unless it is a long wall with no fenestrations (and yes, I had to look it up ) and there are very few problems even on older homes.
    Who's right? Both of you are. You were right for recommending expansion joints, and the builder was right since they are not required.
    From the BIA document:
    SUMMARY OF RECOMMENDATIONS:
    While most examples are for commercial structures, movement joints, although rare,
    also must be considered for residential structures.
    Anybody here could go into a new home and write a 100 pages of item that would be better building practices for every system. It is the builder who is liable for their product, so if it is not required by code then it is the builders discretion.
    Jul 2007
    MH,
    This is brick veneer over frame. Rereading BIA Tech 18a it should have an expansion joint. It clearly says this in the first bullet point under Summary of Recommendations.
    And then, of course, the last line of the Introduction states that movement is rare in SFR. If it gets installed, great. If it doesn't, so be it.
    Joao Vieira's Avatar
    Joao Vieira Guest
    Again without reading the specs, so don't hold me accountable for what i say
    There are commonly known rules for brick veneer control joints. A quick search on google returned this National Concrete Masonry Association (NCMA) Tek Note 10-A, Jerry had another tek note. These vertical control joints will provide movement tolerance between the veneer panels, but we all know that. Usually here in MD I see 30', sometimes a little more.
    An expansion joint is a totally different beast in my experience. It runs though the whole wall assembly, floors and roof. It is mostly used when foundation movement is anticipated. You normally have expansion joints on bridges and long buildings/ structures. If you see the words "expansion joint" in any drawings contact the architect or structural engineer if the expansion joint didn't make it all the way through the building's walls.
    Quote Originally Posted by Joao Vieira View Post
    Why would you not read what has been posted?
    Again,
    Brick veneer= expansion joint
    Concrete= control joint
    As previously mentioned (see post #4)
    From: http://www.gobrick.com/BIA/technotes/t18a.pdf
    An
    expansion joint separates brick masonry into segments to prevent cracking caused by changes in
    temperature, moisture expansion, elastic deformation, settlement and creep. Expansion joints may be horizontal
    or vertical. The joints are formed by leaving a continuous unobstructed opening through the brick wythe that may
    be filled with a highly compressible material. This allows the joints to partially close as the brickwork expands.
    Expansion joints must be located so that the structural integrity of the brickwork is not compromised.
    A
    control joint determines the location of cracks in concrete or concrete masonry construction due to volume
    changes resulting from shrinkage. It creates a plane of weakness that, in conjunction with reinforcement or joint
    reinforcement, causes cracks to occur at a predetermined location. A control joint is usually a vertical gap through
    the concrete or concrete masonry wythe and may be filled with inelastic materials. A control joint will tend to
    open rather than close. Control joints must be located so that the structural integrity of the concrete or concrete
    masonry is not affected.
    Joao Vieira Guest
    Just because is written somewhere does not mean is right I have seen almost all (I believe) types of joint terminology. A building expansion joint will have connections that allow movement of the whole structure, not only the veneer and brick walls.
    In addition to photos, I suggest you to get a drawing detail from the field condition you describe if you want to document properly and request comments/feedback from AR (Architect of Record). I would copy the owner and developer too.
    If AR thinks that a control joint is not required and sends you an email or letter stating so, the liability is on him and you really can't do much about it. If AR does not respond, you can wait for in front of their office and have that match.
    I could not find Tek Note 10-A, would you please post a link for it. Everything I found on this site was related to CMU's not brick veneer.
    Well said.
    Joao Vieira Guest
    here: http://www.prairie-stone.com/docs/tek_note_10-4.pdf
    in there we can find
    Control joint spacing should be
    adjusted where local experience justifies.
    meaning that you can't really go after the Architect of Record or Engineer of Record just because you think he/she is wrong. This does not mean that AR/ER do not make mistakes. We all make mistakes .
    In my experience is better to call the culprit of your anger and ask his opinion about the condition (politely ) . .
    Something like : I was looking at your drawings/building and noticed that there are no control joints. Can you Please explain your thoughts about this condition?
    Is not of your interest to make people mad. It appears that the topic author has done that too. Getting upset sometimes is part of the whole thing.
    BTW: It's funny but happened again to me today. Steel structure with 2" slotted holes at the joist. Static connection from the steel to CMU. CMU had no expansion joint.
