    Default Same scorch, two different panels
    Pic 1 is from a unit I inspected last year, in a 15 year old condo building. The 2nd pic is from the unit next door, same scorch mark.
    Could this be installer error, loose connections?
    Both right side brkrs were 30 amp supplying the dryer.
    Bad batch of breakers?
    Default Re: Same scorch, two panels
    Looks like a breaker may have removed. Possible nearby lightning strike or other strong surge.
    In both panels, the 30 amp breaker for the dryer was replaced with a new breaker further down on the bus bar, and the adjacent breakers on the left side were also moved, apparently by the same repair person, judging from the similar notations on the legends. It's a mystery.
    Lightning strikes to buildings are rare in these parts, too wet for much lightning, lots of trees on the surrounding hills to catch the strike if there is one.
    Denny Waters's Avatar
    Denny Waters Guest
    Perhaps paint contamination of the buses?
    Roger Frazee's Avatar
    Roger Frazee Guest
    John
    Those are commander bolt on breakers. Looks like possible replacement breakers have been installed. Not sure what the breakers for the dryers were??
    Anyway this is very similar to heat damage caused by a failed breaker, though possible to be loose connection. I've seen this same thing in some old style A slimline challenger breakers and murray breakers.
    I'm going to go out on a limb and say failed breaker. Any history you can tell us ? Like tripping problems when operating the dryers?
    Usually a complaint about the breaker tripping out during use of the dryer is common. In most cases the breaker was burned but occassionally the freakin bus was melted also. A loose connection is generally rare with a bolt on style breaker...but also you can strip the threads if you use the grunt method for tightening the hold down screw leaving an iffy connection at best.
    So hard to say.
    I would also be worried about keeping those panels in service...busses look like they took a lot of heat.
    John
    I agree....that is a bad looking bus bar!
    No knowledge, no help from the sellers.
    In both cases, I called for an electrician to check the panels over and verify the bus bars are safe.
    At least one electrician thinks they're fine.
    The electrician is the last man in....you're good to go! Did he just say it or write it down?
