    Default This doesn't look correct

    i inspected a condo today and found this in the service panel. It doesn't look correct, i don't think the terminal/lug is listed for multi / tapps.Not sure and would like input from some of the more experinced HI's. There is no ground bus bar.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: This doesn't look correct

    "Mike"

    Of course its not right.

    Even when a terminal is allowed to have multiple conductors, they have to be of the same size and type.

    You have a large stranded ground and solid wires of differing sizes.

    Never would you find a panel with terminals rated for that many, let alone different types and size conductors in the same terminal.

    It is an unsatisfactory condition and is deficient.


  3. #3
    Join Date
    Mar 2007
    Location
    georgia
    Posts
    112

    Default Re: This doesn't look correct

    The lug should be stamped with the number and size of conductors allowed that lug I would guess from installing many simular lugs only allows one conductor from a #6 to 1/0.


  4. #4
    chris mcintyre's Avatar
    chris mcintyre Guest

    Default Re: This doesn't look correct

    Quote Originally Posted by stanley frost View Post
    There is no ground bus bar.

    One could be added.


  5. #5
    Join Date
    Aug 2009
    Location
    rockport texas
    Posts
    132

    Default Re: This doesn't look correct

    Thanks guy's. Love this site.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: This doesn't look correct

    Quote Originally Posted by chris mcintyre View Post
    One could be added.
    Yes, but it must be a proper ground terminal bar for that enclosure and manufacturer and it must be properly added (most are not when added after the fact to older panels).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    James Duffin's Avatar
    James Duffin Guest

    Default Re: This doesn't look correct

    The only time I call out a grounding lug that has been added is if it has been mounted with sheet metal screws. If it is bolted to the panel or installed into a tapped hole it is installed properly IMHO. That is why lugs are made and sold...to be installed where they are needed.


  8. #8
    Join Date
    Mar 2007
    Location
    South-West Michigan
    Posts
    469

    Post Re: This doesn't look correct

    I will agree that there should be a ground bus, and this lug should not be used this way. Is this a subpanel?

    Randall Aldering GHI BAOM MSM
    Housesmithe Inspection
    www.housesmithe.com

  9. #9
    Join Date
    Aug 2009
    Location
    rockport texas
    Posts
    132

    Default Re: This doesn't look correct

    Randy,
    Yes it's a "sub panel" The main service panel was a nightmare. enclosed in an exterior utility closet, Appox 10' off the ground and i couldn't get in to look at it & 1970's FPE panel. You can imagine the shape it was in, this unit is next to the Gulf of Mexico.


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: This doesn't look correct

    Quote Originally Posted by Randy Aldering View Post
    Is this a subpanel?

    Nope, looks like it is in a house to me, that makes it a "house panel".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Aug 2009
    Location
    rockport texas
    Posts
    132

    Default Re: This doesn't look correct

    Bill, It was written up. As you can see in the pic. there wasn't room for me to get my head in the closet ( the main panel is above the meter all the way to the left). I don't understand why they let them do it like this around here but I see it more often than not.