    Default Wanted to double check this breaker

    Just wanted to double check to see if this breaker is okay for two conductors. The installer was the home owner who was an electrician, he said it was, It doesnt look like it to me, however.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Nov 2009
    Location
    St Paul, MN
    Posts
    1,630

    Default Re: Wanted to double check this breaker

    No, it's not.

    MinnesotaHomeInspectors.com
    Minnesota Home Inspectors LLC
    ASHI #242887 mnradontesting.com

  3. #3
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Wanted to double check this breaker

    I thought so. I thought because he was an electrician he knew something I was unaware of.
    Thanks Ken


  4. #4
    Join Date
    Nov 2009
    Location
    St Paul, MN
    Posts
    1,630

    Default Re: Wanted to double check this breaker

    From my experience electricians have the most hazardous wiring in their own homes.

    MinnesotaHomeInspectors.com
    Minnesota Home Inspectors LLC
    ASHI #242887 mnradontesting.com

  5. #5
    Join Date
    Mar 2007
    Location
    Ft. Myers, FL
    Posts
    363

    Default Re: Wanted to double check this breaker

    The blue wire going to the buss bar is nice too.