    Sep 2008
    so so, California
    Default Wut's up with this vent?
    So this vent is from a water heater, viewed from the second story. It terminates 5 feet from this operable window and less than that from that wall to the right. From what I understood, the vent must terminate above the roof when less than 8 feet from the wall (I thought it was 5'), and then there is this window.
    G2427.6.3 (503.6.4) Gas vent termination.
    A gas vent
    shall terminate in accordance with one of the following:
    1. Gas vents that are 12 inches (305 mm) or less in size
    and located not less than 8 feet (2438 mm) from a vertical
    wall or similar obstruction shall terminate above
    the roof in accordance with Figure G2427.6.3.
    Default Re: Wut's up with this vent?
    Correct-- it can't be within 8' of the sidewall. When it gets extended, it must extend up a min. of 2' above the upper roof line as well.
    Sep 2008
    so so, California
    Interresting...you have to wonder how an entire housing track got away with this.
    Thanks BW
    I believe you are not reading the correct code
    2. Gas vents that are over 12 inches (305 mm) in size or
    are located less than 8 feet (2438 mm) from a vertical
    wall or similar obstruction shall terminate not less
    than 2 feet (610 mm) above the highest point where
    they pass through the roof and not less than 2 feet (610
    mm) above any portion of a building within 10 feet
    (3048 mm) horizontally
    Sep 2008
    so so, California
    Over, under 12"...Isn't the vertical wall issue still applicable?
    Brandon, Obviously it can be w/i 8' because someone did it. But I know what you meant.
    There is a difference
    The photo shows it IS LESS than 8'
    Since it IS LESS than 8', then rule 2 applies
    Sep 2008
    so so, California
    ooh yes, I had to read that twice and slowly. I hate the way code is written.