    Is it ok for a drain line from a bathroom to cross through the return air duct?

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: Sewer line thru return air duct

    I see this all the time in older houses (and some newer ones too). It's not a good idea. If there is a leak on the drain line and into the return air duct, the air stream in the house and the return duct is now contaminated.

    Return ducts should be just that....return ducts for the HVAC system. Not chases to run wires or pipes.

    "It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey

  3. #3
    Join Date
    Jul 2008
    Location
    Utah
    Posts
    390

    Default Re: Sewer line thru return air duct


    The major problem with running a pipe thru a duct is the obstruction to the airflow. It was (probably) sized for a given flow and if you obstruct you may mess up that system as well.