    Default 2 Panels in a closet converted garage
    This one went over my head.
    Panel on the left 200 amp main Set for the home Interior. Bonded
    Panel on the right 225 amp main set up for the pool house, AC, Carport. not bonded.
    Location interior of a converted garage in a wall closet behind a painting.
    The Service is from a Large solar system down the hill from the home 5000 S.Q. Foot home.
    Everything points to a non permitted job.
    Photo # 9528 225 amp panel on right
    photo # 9516 220 amp panel on left
    photo # 9529 225 amp panel on right
    What do you think.
    Best
    Ron
    Crawl Space Creeper
    Default Re: 2 Panels in a closet converted garage
    Quote Originally Posted by Ron Bibler View Post
    Explain "bonded".
    Do you mean 'the neutral is bonded to ground' and 'neutral is not bonded to ground'?
    Or do you mean the enclosures are, or are not, bonded to ground?
    Ron Bibler's Avatar
    Ron Bibler Guest
    Quote Originally Posted by Jerry Peck View Post
    The enclosures are, and are not, bonded to ground?
    Best
    Ron
    Jul 2008
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Ron,
    Separately Derived Systems | IAEI Magazine Online
    Separately Derived Systems, IAEI Magazine August 2009
    and
    KDER Guide Info from UL
    KDER.GuideInfo - Grounding and Bonding Equipment
    Note Links to QIGU for PV Systems and subsequent links.
    See Art. 690.
    Ron Bibler's Avatar
    Ron Bibler Guest
    Quote Originally Posted by H.G. Watson, Sr. View Post
    Ron,
    and
    See Art. 690.
    Thanks HG. Good info... These panels and the complete system has no permit. After talking to the buyers agent he told me that the seller had stated these little facts along with the complete Garage convertion...
    Best
    Ron