Aluminum- Copper pigtail
The splice in this panel has me a little concerned. By the size and shape of the tape wads I would have to guess they are wire nuts and not copalum crimp splices. The house was built in 2000 and I think the purple wire nuts were code compliant at the time (and may still be), but can't tell if they are the Ideal #65 type or not.
There have been several threads regarding the different splices and the purple Ideal #65 is known to have failed.
What, if anything would you put in the report?
Thanks in advance.
Similar Threads:The beatings will continue until morale has improved. mgt.
-
09-13-2010, 12:53 PM #2
Re: Aluminum- Copper pigtail
It looks like they used a split bolt to change from alum to copper so the wire would fit on a 30 amp breaker. The only concern, if any, would be if they used a copper to alum split bolt. If I saw that and the rest of the panel looked OK I would not say anything.
Lot's of time the electrician does not know what is going to be installed so they run a wire to handle most anything. I bet this circuit is for an outside condensing unit or heat pump.
-
09-13-2010, 01:35 PM #3
-
09-14-2010, 08:18 AM #4
Re: Aluminum- Copper pigtail
Just for argument sake...
Assumming both wires are copper, is there an approved wire nut that would handle the two different wire sizes?
And you have 2 breakers feeding a single wire with the lower splice. Turn off one breaker and the wires are still engerized.
Get a sparky in there.
Last edited by Bruce Ramsey; 09-14-2010 at 08:26 AM.
"The Code is not a peak to reach but a foundation to build from."
-
09-14-2010, 08:43 AM #5
Re: Aluminum- Copper pigtail
-
09-14-2010, 01:28 PM #6
Re: Aluminum- Copper pigtail
Why the splice? A 30 amp QO breaker will accept 8 awg al/cu.
-
09-14-2010, 01:49 PM #7
Re: Aluminum- Copper pigtail
Maybe it is a #6?
-
09-14-2010, 02:02 PM #8