    Default Possible Undersized Main Service Breaker

    Hi:

    It appears that this 100-amp breaker is mismatched in size with an aluminum service wire.

    Can anyone tell if this wire is tinned copper?
    If this wire is tinned copper, is it sized correctly?

    Thanks,
    Joe

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Possible Undersized Main Service Breaker

    Quote Originally Posted by Joe Arcaro View Post
    Hi:

    It appears that this 100-amp breaker is mismatched in size with an aluminum service wire.

    Can anyone tell if this wire is tinned copper?
    If this wire is tinned copper, is it sized correctly?

    Thanks,
    Joe
    The service conductors may be tinned copper, because the insulation is likely rubber under the cloth. Can't tell the gauge. That whole panel install is poorly done, with a large knockout missing on the right, missing cable clamp, amateur workmanship. Along with that flaky feeder to the water heater, there's work for an electrician there.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  3. #3
    John Steinke's Avatar
    John Steinke Guest

    Default Re: Possible Undersized Main Service Breaker

    I'm not sure I understand your question.

    That is ... so what if the wires are larger than you expect? As long as they fit in the breaker lugs, there's no problem. To carry it to an extreme, you could have 500MCM wires feeding a 15-amp breaker.

    Or, are you asking are the wires too small? Well, if this is the main disconnect, then the wires are under the exclusive control of the utility, and thus the NEC does not apply - read the introduction (Article 90) - regardless of whatever other tables and references you might find in the NEC. The PoCo sizes wires / services by their own standards.


  4. #4
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Possible Undersized Main Service Breaker

    Quote Originally Posted by John Steinke View Post
    ? Well, if this is the main disconnect, then the wires are under the exclusive control of the utility, and thus the NEC does not apply - read the introduction (Article 90) - regardless of whatever other tables and references you might find in the NEC. The PoCo sizes wires / services by their own standards.
    It is my understanding that the power company stop at the top of the meter and from the bottom of the meter forward falls under the NEC....at least in the areas I work in.


  5. #5
    John Steinke's Avatar
    John Steinke Guest

    Default Re: Possible Undersized Main Service Breaker

    Really? Then how would you work on these wires without breaking the utility's seal? What amperage would you assign the feed? How would you applytap rules?