    Question what to use under vinyl siding romex simplull, BX, Conduitit + NYC Code?

    Electrical for lights exterior Under vinyl siding what is within code in NYC regarding electrical for lights.?
    ROMEX BRAND SIMPULL, BX, or CONDUITIT.
    And why.
    Also what is advantages and disadvantages of each under vinyl siding.
    i WAS TOLD A NAIL OR SCREW CAN GO THROUGH ROMEX AND NOT WITHIN CODE AND TOLD IT IS WITHIN CODE, TOLD BX IS NOT FOR WET AREAS AND IT GETS WET UNDER VINYL SIDING THEN TOLD IT CAN BE USED. THE CONDUITIT DOESN'T FIT UNDER VINYL SIDING TO THICK BUT I KNOW THAT IS WITHIN CODE IN NYC.
    PLEASE IF YOU HAVE THIS INFO. ANSWER AS SOON AS POSSIBLE.
    nEW TO COMPUTERS AND IT TOOK 2 HOURS TO FIND HOW TO PUT THIS IN. i AM NOT SURE HOW TO FIND ME RESPONCE. could you give me an idea how to see response.

    THANKS

    Similar Threads:
    Last edited by Barbara Lande; 10-18-2010 at 01:11 PM.
    OREP Insurance

  2. #2
    Philip's Avatar
    Philip Guest

    Default Re: what to use under vinyl siding romex simplull, BX, Conduitit + NYC Code?

    [quote=Barbara Lande;147879]Under vinyl siding what is within code in NYC regarding electrical for lights.?
    ROMEX BRAND SIMPULL, BX, or CONDUITIT.
    And why.
    Also what is advantages and disadvantages of each under vinyl siding.
    i WAS TOLD A NAIL OR SCREW CAN GO THROUGH ROMEX AND NOT WITHIN CODE AND TOLD IT IS WITHIN CODE, TOLD BX IS NOT FOR WET AREAS AND IT GETS WET UNDER VINYL SIDING THEN TOLD IT CAN BE USED. THE CONDUITIT DOESN'T FIT UNDER VINYL SIDING TO THICK BUT I KNOW THAT IS WITHIN CODE IN NYC.
    PLEASE IF YOU HAVE THIS INFO. ANSWER AS SOON AS POSSIBLE.
    nEW TO COMPUTERS AND IT TOOK 2 HOURS TO FIND HOW TO PUT THIS IN. i AM NOT SURE HOW TO FIND ME RESPONCE. could you give me an idea how to see response.
    None of the above. You do not put any wiring under the siding.


  3. #3
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: what to use under vinyl siding romex simplull, BX, Conduitit + NYC Code?

    This post is a joke, right?
    As Philip mentioned, don't install any of it under the vinyl siding. Install inside of walls or surface mount using approved materials. If a guy tells you its Ok to put electrical under vinyl siding, ask to see his electrical license.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: what to use under vinyl siding romex simplull, BX, Conduit + NYC Code?

    As the others have said: put the wiring IN the wall, and to continue with that idea ... NM cable (RomexTM is just one brand of NM cable) *IS NOT* allowed to be used outdoors, not even if in conduit.

    The NM cable would need to end in an interior junction box and a wiring method approved for use outdoors would then need to be connected to the NM cable and run outdoors.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: what to use under vinyl siding romex simplull, BX, Conduitit + NYC Code?

    In re: "What to use under vinyl siding romex simplull, BX, Conduitit +NYC Code?"

    What to use? A NYC licensed Electrical Contractor and a valid permit.

    NYC doesn't allow electrical installation by anyone else.