    Default Can AFCI breaker have two wires?

    Can the AFCI breaker have two hot wires installed into one lug? Thanks

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Can AFCI breaker have two wires?

    The lug on the breaker is listed for a single conductor. The correct way to wire this would be to install a pigtail on the breaker and wire nut the 2 conductors to it.

    This "fix" appears to have been made to Get AFCI protection on a multiwire branch circuit. GE makes a new style AFCI that can be used on this type circuit - two are used and only one requires the neutral connection, but a handle tie is required between the two.


  3. #3
    Join Date
    Apr 2008
    Location
    Western Massachusetts
    Posts
    536

    Default Re: Can AFCI breaker have two wires?

    You should also note whether that Siemens AFCI breaker is allowed to be used in that enclosure.


  4. #4
    Join Date
    Oct 2010
    Location
    Southwest US
    Posts
    585

    Default Re: Can AFCI breaker have two wires?

    Quote Originally Posted by Bill Kriegh View Post
    The lug on the breaker is listed for a single conductor. The correct way to wire this would be to install a pigtail on the breaker and wire nut the 2 conductors to it.

    This "fix" appears to have been made to Get AFCI protection on a multiwire branch circuit. GE makes a new style AFCI that can be used on this type circuit - two are used and only one requires the neutral connection, but a handle tie is required between the two.
    If that's a multiwire circuits, the double tap is the least of the problems. With the circuits on the same phase the neutral will be overloaded. The fix for sure wound not be to pigtail the circuits together!


  5. #5
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Can AFCI breaker have two wires?

    Quote Originally Posted by Benjamin Thompson View Post
    If that's a multiwire circuits, the double tap is the least of the problems. With the circuits on the same phase the neutral will be overloaded. The fix for sure wound not be to pigtail the circuits together!
    That would be true if the two hot wires were on separate breakers. Since they are on the same breaker the neutral won't see an overload. If the AFCI was a 20 AMP variety there might be an issue depending on the circuit conductors size.


  6. #6
    Join Date
    Oct 2010
    Location
    Southwest US
    Posts
    585

    Default Re: Can AFCI breaker have two wires?

    Good point, I "forgot" about the circuit breaker that would trip in an overload situation.
    I guess if you consider what an AFCI breaker is supposed to do, there wouldn't be a problem connecting 2 wires as the issue with 2 wires is arcing. If you are going to double tap a breaker, the AFCI would be the one to double tap.


  7. #7
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Can AFCI breaker have two wires?

    The default rule is ONE per terminal, connector, lug, etc. when it comes to conductors; UNLESS INDICATED for more than one. INDICATED means marked or labeled.