Results 1 to 11 of 11
  1. #1
    Join Date
    Mar 2009
    Location
    Charlottesville, Va.
    Posts
    300

    Default Cutler Hammer breaker identification help

    I know some Square D and I think some Cutler Hammer circuit breakers are designed for 2 conductors but, I don't see much Cutler Hammer equipment and I don't know if these circuit breakers are designed/rated for 2 conductors or not. On Square D equipment I can always see the contact plate designed for 2 conductors but I can't see anything on these.

    I tried reading the breaker labels on site and at home with photo editing, but my eyes are not what they used to be...I really need to add a good magnifying glass to my tool bag.

    Can anyone more experienced than I tell me if these are rated for 2 conductors?

    Thanks.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Charlotte NC Licensed in NC and SC
    Posts
    597

    Default Re: Cutler Hammer breaker identification help

    They are for one conductor only. The dual type will always have seperation between the wires with a double saddle.

    Bruce King, B.A. King Home Inspections, LLC
    www.BAKingHomeInspections.com
    Certified Master Inspector, Independent Inspectorwww.IndependentInspectors.org

  3. #3
    Join Date
    Mar 2009
    Location
    Charlottesville, Va.
    Posts
    300

    Default Re: Cutler Hammer breaker identification help

    Thank you Bruce...


  4. #4
    Bruce Hutton's Avatar
    Bruce Hutton Guest

    Default Re: Cutler Hammer breaker identification help

    I agree...Thats a double tap for sure!

    Imagine not removing the panel covers & missing this.

    I went ot a continuing ed class over the summer & there were 3-4 inspectors out of 20 that said they do not remove the covers.


  5. #5
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Cutler Hammer breaker identification help

    The answer to the question is what type of breaker this is. If it is a type CH it is listed for 2 wires if the wire sizes are #14 - #10.


  6. #6
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Cutler Hammer breaker identification help

    Quote Originally Posted by Bill Kriegh View Post
    The answer to the question is what type of breaker this is. If it is a type CH it is listed for 2 wires if the wire sizes are #14 - #10.
    The brown handle confirms that they are CH breakers. The plastic mounting foot means these are the newer style that is available now on the shelves. The older style had a metal foot.


  7. #7
    Join Date
    Mar 2009
    Location
    Charlottesville, Va.
    Posts
    300

    Default Re: Cutler Hammer breaker identification help

    Thanks for the additional replies.

    They are CH type....my photo editing and vision quality allow me to determine that...but googling Cutler Hammer CH breaker specifications has yet for me to find it in writing that they are listed for two conductors.

    I'll keep trying as time allows.....


  8. #8
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Cutler Hammer breaker identification help

    If you click the link above for checking the types of wire allowed you will be on a CH catalog page that also shows that 2 wires are permissible in sizes #14 - #10. Incidently, this is the only way you could have a mix of solid and stranded..........

    I posted that link because it provides a place to see what the specs are and provide answers to what are frequent questions here, at least on CH type breakers. Further research on this and other catalog sites will provide info on neutral/ground buss bars and permitted wire combinations. There are also things you probably haven'y seen yet, like AFCI breakers that clip onto a neutral buss as well as a line buss and consequently don't have a neutral pigtail.

    All the current manufacturers have this type of catalog page on line.


  9. #9
    Join Date
    Mar 2009
    Location
    Charlottesville, Va.
    Posts
    300

    Default Re: Cutler Hammer breaker identification help

    I'm not seeing your link, but it sounds like just what I need to read and look forward to it's appearance.


  10. #10
    Join Date
    Mar 2007
    Location
    Fuquay Varina, NC
    Posts
    1,074

    Default Re: Cutler Hammer breaker identification help

    Pull the two and pig tail it with a wire and nut and single wire it back. Ask a AHJ (another thread) and they will walk the home owner on how to change

    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com

  11. #11
    Tony Peluso's Avatar
    Tony Peluso Guest

    Default Re: Cutler Hammer breaker identification help

    hyugtf


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •