    Default Residential Main Breaker Tap

    Can the line side of a residential service main breaker be tapped if listed and feed main breaker of 2nd panel to create pole spaces ? Please list article to support response.

    Thanks

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Residential Main Breaker Tap

    If you are asking about two conductors terminated in the lugs of the main breaker, the answer is no. Few breaker brands are listed to accept two conductors and this is typically in the 15-30 amp sizes. Larger breakers are for one conductor.

    A pic would help.


  3. #3
    Dennis Thatcher's Avatar
    Dennis Thatcher Guest

    Default Re: Residential Main Breaker Tap

    2008 NEC 240.21(B)(2) Would appear to allow this application, however; there are 3 requirements that have to be met. I'll leave it to the professional electricians to explain the fine details.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Residential Main Breaker Tap

    Quote Originally Posted by Trent Posner View Post
    Can the line side of a residential service main breaker be tapped
    Quote Originally Posted by Dennis Thatcher View Post
    2008 NEC 240.21(B)(2) Would appear to allow this application, however; there are 3 requirements that have to be met. I'll leave it to the professional electricians to explain the fine details.
    That NEC section is not relevant to the question. That section is about "taps" to feeders ... the question was about multiple tapping a breaker.

    Multiple tapping a breaker is a function of the rating of the terminals on the breaker, and it is highly unlikely (as Jim pointed out) that the breaker would be rated for multiple taps with conductors that large.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Feb 2009
    Location
    On The Mason-Dixon Line
    Posts
    577

    Default Re: Residential Main Breaker Tap

    The original post can be read 2 ways

    One way is: Is he asking about double tapping the lugs on the line side of the main breaker?

    OR

    Another way is: Is he asking if it is allowed to tap the feed going to line side of the main breaker ( aka: a feeder tap )

    Trent please clarify