Results 1 to 5 of 5
  1. #1
    Andy Jarchow's Avatar
    Andy Jarchow Guest

    Default Is this an old tpr valve?

    Hello all,

    This was just above a water heater that was installed in 08. Is this an old tpr valve?

    If not what is it?

    Thank you

    mk

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Is this an old tpr valve?

    Quote Originally Posted by Mike Krueger View Post
    Hello all,

    This was just above a water heater that was installed in 08. Is this an old tpr valve?

    If not what is it?

    Thank you

    mk
    It is not a TPR valve. TPR valves have a probe that goes into the tank.

    It could be an expansion relief valve. Used in place of an expansion tank. If that is what it is (does not look like any I have seen) it needs to have a discharge line attached to it.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Andy Jarchow's Avatar
    Andy Jarchow Guest

    Default Re: Is this an old tpr valve?

    Quote Originally Posted by Scott Patterson View Post
    It is not a TPR valve. TPR valves have a probe that goes into the tank. Good point!

    It could be an expansion relief valve. Used in place of an expansion tank. If that is what it is (does not look like any I have seen) it needs to have a discharge line attached to it.
    Yes it does have a discharge line so it might be expansion relief valve.

    Thank you for the info Scott
    mk


  4. #4
    Widdershins Saunders's Avatar
    Widdershins Saunders Guest

    Default Re: Is this an old tpr valve?

    Quote Originally Posted by Mike Krueger View Post
    Yes it does have a discharge line so it might be expansion relief valve.

    Thank you for the info Scott
    mk

    It looks like an adjustable pressure relief valve to me.

    Most TPR's are set to pop off at 150psi or at 210 degrees -- In instances where it is impractical to run the TPR outside or to an indirect receptor, a Plumber will install a pressure only relief valve, usually set to pop off at 125psi on the cold water line.

    Usually high enough to allow the discharge to gravity drain to the ground outside.


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: Is this an old tpr valve?

    To clarify what has been said in the posts above: TPR or T&P are "combination" 'temperature and pressure' relief valves, that valve is 'pressure' only (and thus sometimes used for as a thermal expansion relief valve, but the better solution is to install a thermal expansion tank).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •