Results 1 to 18 of 18
Thread: Challenger circuit breker help
11-16-2010, 10:09 AM #1
I'd like some help positively determining if these Challenger 20 amp circuit breakers are rated for two conductors. I don't believe they are because pressure is applied to the conductor(s) with just the end of the screw and not a pressure plate of any kind.
I've googled as best as time allows right now, even entering the below numbers in one of the part listings at one of the large electrial sites....no luck yet on my end...the change of ownership and branding sure doesn't help. The houses were built in 1998...big estate three houses.
Here's the data off the breaker.
Type C120
HACR type
1 pole J969
E7S19-T-92 02 18
LR43556
Thanks for the help.
11-16-2010, 10:41 AM #2
Re: Challenger circuit breker help
Try Here Challenger C120 Circuit Breakers | RELECTRIC
11-16-2010, 11:06 AM #3
Thanks....I tried the data sheets there. They only load as single pages which is frustrating and some of them don't load at all for me. The geelectric name is on those data sheets whose ownership post dates the period when these houses were constructed, according to info. I read on another site.
11-16-2010, 12:19 PM #4
Your not going to find much on the web about challenger breaker specs. Your best bet is to take a look on the side of the breakers molded case. Some breakers will have the # of conductors allowed for the terminal located there with a little embossed diagram of the compression terminal.
Not having that you must assume only one conductor ... the type terminal you have usually will not accept two conductors.
If you go to this link you get your answer on page 12 .. line 18 ..titled Multiple Conductor Connectors. I'd bookmark the link it gives you a lot of useful information about circuit breakers that you will use quite often.
http://ewh.ieee.org/r6/san_francisco...t_Breakers.pdf
11-16-2010, 12:34 PM #5
Billy's, information answered the question, definitively.
mf.
Matt Faust
Real Estate Inspector
11-16-2010, 12:45 PM #6
11-16-2010, 01:19 PM #7
Thank you for the link Roger...downloaded a copy to my ever expanding reading list.
I recently purchased a magnifying glass and added it to my toolbag to help with reading the sides of circuit breakers. These Challengers had no markings, that I could interpret, indicating they were listed for 2 conductors, but I like to be thorough so was searching for additional confirmation.
I took Matts post as sarcastic...but maybe I was wrong...
11-16-2010, 02:10 PM #8
11-16-2010, 02:55 PM #9
I can't say for sure, but the connector looks like it was made to accept 2 conductors.
11-16-2010, 05:18 PM #10
Re: Challenger circuit breaker help
Roger,
I'll throw some mud up on the window and see if the window comes clearer ...
The wire size *IS* specified in those pages ... the wire size *IS* specified as 14-10 AWG ... nothing in there about 'more than one' 14-10 AWG, thus that leaves us at 'just one' is allowed.
After all, the NEC does say "Terminals for more than one conductor ... shall be so identified.", and not "so identified" then only one conductor is allowed.
11-16-2010, 06:55 PM #11
From the UL Marking Guide for MCCBs (Molded Case Circuit Breakers) more recent than Roger's 2002 version:
Multiple Conductor Connectors - If the terminals of a circuit breaker are acceptable for use with multiple connections in one hole, and the breaker is intended for this type of use, the breaker is marked to indicate the proper multiple connections. This is uncommon for breakers -- ordinarily, the terminals are suitable for only one wire per hole.
HTH.
11-16-2010, 07:21 PM #12
That wasn't that muddy. I saw the wire size just not the # of wires....
I do get what your adding though. Forgot the language in the NEC. I gotta get a new 2008 (or break out an older edition) ..after being on this forum these past months the binding has deteriorated ( from opening and closing) so that several dozen of the pages have fallen out and it is in disarray....
11-16-2010, 07:23 PM #13
11-16-2010, 08:19 PM #14
11-17-2010, 07:56 PM #15
I'm not sure if that was sarcasm...or confusion???
The text quoted IS original as to the 2008 UL Marking Guide for MCCBs, I highlighted portions using red and underlining for emphasis, the emphasis was mine; the bold was original, as was the text.
One terminal, one hole, one conductor; unless expressly noted ("indicated") on the device and terminal otherwise, for any CB less than 100A. NEC defaults with same "one terminal - one conductor" connection, unless indicated/marked otherwise - Chapter 1, Section 110.14, subsection(A), second paragraph especially:
Originally Posted by NEC 110.14(A)
11-17-2010, 08:26 PM #16
11-17-2010, 08:55 PM #17
Correct me if I'm wrong.
Square D (the newer versions) and
Cuttler Hammer type CH
are the ONLY breakers which can have two wires under one screw.
Right?
11-17-2010, 11:31 PM #18
Those are listed for 2 ...yes. It would be best to look at it this way .. if the breaker is marked for 2 conductors then 2 conductors it is. If not then only one.
It would be nice if a list was out there that is verifiable that would specify the breakers that accept two conductors.
You often here the argument it must be installed to the manufacturers instructions ... true NEC 110.3b says so .... when was the last time you saw instructions come with a breaker....??