    Default Electrical cables contacting each other

    Last edited by Scott Lynch; 12-20-2007 at 04:26 PM.
    Crawl Space Creeper

  2. #2
    Brian E Kelly's Avatar
    Brian E Kelly Guest

    Default Re: Electrical cables contacting each other

    What are the cables in question? Power and control wiring ?


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Electrical cables contacting each other

    That's called "bundling" and causes those to need to be derated. 4-6 conductors are to be derated to 80%, which would still be on a 15 amp breaker.

    Not that I like it, but with just those two there, I would write it up, but not make a big deal about it. It will likely not affect the furnace, and the attic light will be nowhere near rated amperage for that circuit, so derating would not affect the attic light at all.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com