    Question Service panel conversion

    I inspected a house today that has on old service panel that had been converted from fuses to breakers. The panel is being used, but not as the main service panel. It was originally rated at 30 amps and it appears to have 30 amp service wires entering it. I am recommending a licensed electrician further evaluate. Has any one seen this type of conversion before?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: Service panel conversion

    Quote Originally Posted by Trent Tarter View Post
    I am recommending a licensed electrician further evaluate.
    The proper recommendation is "Fuse panel interior was replaced with a breaker panel interior, now the entire panel, interior and enclosure, need to be replaced."

    You are just asking for trouble with a Capital T if you defer to an electrician and do not make the call yourself.

    Has any one seen this type of conversion before?
    Many times. Replace the panel.

    If you call for a replacement and the electrician says otherwise, then something happens *YOU* *STILL* called for replacement - the electrician is on the hook, not you.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Nampa, Idaho
    Posts
    601

    Thumbs up Re: Service panel conversion

    Thanks Jerry