Results 1 to 17 of 17
  1. #1
    Join Date
    Mar 2007
    Location
    Oklahoma City
    Posts
    357

    Default LP Gas Tank Installation

    Is there a code that prohibits a propane gas tank from pointing at the structure. I could have sworn I had something on this but cannot find it. I called it on a home today and the seller's propane supplier says that it does not matter which direction the ends are pointing.

    Similar Threads:
    OREP Insurance
    If it weren't for lawyers, we would never need them.

  2. #2
    Join Date
    Mar 2007
    Location
    Oklahoma City
    Posts
    357

    Default Re: LP Gas Tank Installation

    I thought I saw something about this on here before but can't find anything.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    If it weren't for lawyers, we would never need them.

  3. #3
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: LP Gas Tank Installation

    NFPA 58 can be viewed on-line. Visit NFPA.org, click on List of Codes and Standards, scroll down to NFPA 58 and review. Here is a direct link to the 2011 edition.

    http://www.nfpa.org/aboutthecodes/Ab....asp?DocNum=58

    If you're looking at the current edition, start with chapter 6 (when the document loads in the real viewer window, click on "TOC" for an interactive jump list to the chapters.


    You might also check what your local codes and fire suppression review for the property/neighborhood density, etc. have to say on the subject.

    Last edited by H.G. Watson, Sr.; 01-27-2011 at 10:10 AM.

  4. #4
    Join Date
    Apr 2007
    Location
    state of jefferson
    Posts
    522

    Default Re: LP Gas Tank Installation

    pointing is impolite, but not a fire code violation.


  5. #5
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: LP Gas Tank Installation

    I see no cause for alarm there. Those tanks are often leased from the supplier, so that is where they chose to locate the tank, accessible for filling, at a proper distance.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  6. #6
    Join Date
    Mar 2007
    Location
    Oklahoma City
    Posts
    357

    Default Re: LP Gas Tank Installation

    I guess I must have dreamed it or something. There must be something to it though, because you almost never see them pointed at the structure. At least not around here.

    If it weren't for lawyers, we would never need them.

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: LP Gas Tank Installation

    The usual reason, probably (as I am guessing as to the usual reason), is one of clearances from the structure and the property line.

    With the tank turned parallel with the house and the property line, less land will meet the required clearances as the tank is 'shorter' when installed parallel with the house and property line.

    In this case, where there may be a larger yard area, they may have wanted to 'see' less of the tank looking out the windows, so the tank was installed perpendicular to the house wall to present a smaller profile when viewed from the house.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Oct 2010
    Location
    Southwest US
    Posts
    585

    Default Re: LP Gas Tank Installation

    Quote Originally Posted by brian schmitt View Post
    pointing is impolite, but not a fire code violation.
    Besides, how do you know it isn't pointing away from the structure?
    Some of the older tanks used to be "end fill" with the valve on one end, maybe these couldn't be pointed at the house??

    Last edited by Benjamin Thompson; 01-27-2011 at 07:15 PM.

  9. #9
    Join Date
    Mar 2009
    Location
    Charlottesville, Va.
    Posts
    300

    Default Re: LP Gas Tank Installation

    I've heard this too so I called my local LP supplier about this awhile back.

    I was told that yes, some towns do require that either end of the horizontal cylinder type LP tanks do not point directly at any dwelling. The reason given to me was that if the tanks rupture the end caps can blow off and become a projectile.


  10. #10
    Join Date
    Mar 2007
    Location
    Oklahoma City
    Posts
    357

    Default Re: LP Gas Tank Installation

    Yes, that is what I have always heard. The ends will shoot out like a bullet, thus they should not be pointed at the structure from either end.

    If it weren't for lawyers, we would never need them.

  11. #11
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: LP Gas Tank Installation

    Quote Originally Posted by Frank Bombardiere View Post
    Yes, that is what I have always heard. The ends will shoot out like a bullet, thus they should not be pointed at the structure from either end.

    You would not want the house damaged before the fire starts.


  12. #12
    Join Date
    Oct 2010
    Location
    Southwest US
    Posts
    585

    Default Re: LP Gas Tank Installation

    Quote Originally Posted by Garry Sorrells View Post
    You would not want the house damaged before the fire starts.
    If the tank explodes, the fire is already well underway!


  13. #13
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: LP Gas Tank Installation

    Quote Originally Posted by Frank Bombardiere View Post
    Yes, that is what I have always heard. The ends will shoot out like a bullet, thus they should not be pointed at the structure from either end.
    That makes sense. We know water heaters tend to blow at the ends. Sounds like the Mythbusters need to blow up a Fat Boy full of propane.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  14. #14
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: LP Gas Tank Installation

    Tanks have pressure relief valves so they vent upwards. If there is a fire, you will have one heckova blowtorch but it sill simply burn itself out after awhile. I've watched many tanks do this from house fires.

    The only real danger is from a BLEVE-Boiling Liquid Expanding Vapor Explosion. Just Google it for videos. If you have a flame impinging on the tank at or below the liquid level, it will simply vent as above. However, if you have a flame impinging at the upper part of the tank, it will create enormous pressure while weakening the tank. When the upper tank ruptures at the point of impingement, you have a massive fireball the size of a city block. Note it blows out at the site of impingement-it doesn't blow out the ends every time. In fact, the ends are much stronger than the top of the cylinder. Now, when LP gas boils at -44F, it expands 277 times so you get an impressive little fireball.

    If this theory about the ends of LP tanks being so dangerous then why don't they make bobtail delivery trucks with cylinders pointed to the sky and roadway? Does this mean you are in danger of following right behind these trucks? This is silly. Sorry,

    Keep the fire in the fireplace.

  15. #15
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Re: LP Gas Tank Installation

    From a physics stand point ..... If the tank was completely without safety features and the pressure was such that the tank would rupture, by design and shape of this vessel, it would rupture along the seam of the cylinder -- NOT the end caps.

    Ken Amelin
    Cape Cod's Best Inspection Services
    www.midcapehomeinspection.com

  16. #16
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: LP Gas Tank Installation

    Quote Originally Posted by Bob Harper View Post
    Tanks have pressure relief valves so they vent upwards. If there is a fire, you will have one heckova blowtorch but it sill simply burn itself out after awhile. I've watched many tanks do this from house fires.

    The only real danger is from a BLEVE-Boiling Liquid Expanding Vapor Explosion. Just Google it for videos. If you have a flame impinging on the tank at or below the liquid level, it will simply vent as above. However, if you have a flame impinging at the upper part of the tank, it will create enormous pressure while weakening the tank. When the upper tank ruptures at the point of impingement, you have a massive fireball the size of a city block. Note it blows out at the site of impingement-it doesn't blow out the ends every time. In fact, the ends are much stronger than the top of the cylinder. Now, when LP gas boils at -44F, it expands 277 times so you get an impressive little fireball.

    If this theory about the ends of LP tanks being so dangerous then why don't they make bobtail delivery trucks with cylinders pointed to the sky and roadway? Does this mean you are in danger of following right behind these trucks? This is silly. Sorry,
    Quote Originally Posted by Ken Amelin View Post
    From a physics stand point ..... If the tank was completely without safety features and the pressure was such that the tank would rupture, by design and shape of this vessel, it would rupture along the seam of the cylinder -- NOT the end caps.
    Thanks, Bob and Ken, I'm posting a couple of BLEVE links here. I imagine the theory is that the welded seams would let go first, but as you say, most likely it would be the valves blowing out first and the rupture starting there.


    YouTube - BLEVE (Boiling Liquid Expanding Vapor Explosion) Demonstration - How it Happens Training Video

    YouTube - Mexico BLEVE Explosion

    I took this pic a few years back, practicing with my paint pole cam. This tank was not pointing at my house. It was pointing at the power pole to the left and my neighbor's house on the right. Glad I got rid of it.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by John Kogel; 01-29-2011 at 02:17 PM.
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  17. #17
    Jack Murdock's Avatar
    Jack Murdock Guest

    Default Re: LP Gas Tank Installation

    per NFPA 58 if that tank is 500 gallon wc or left it can be 10 feet from the house and / or property line. The point of transfer requirement is also 10 feet from any source of ignition. As a rule in the 30+ years I have worked in the gas industry both LP and Natural we didn't point the bullet end at a structure. Vehicles are more of a threat but the closer the tank is to the house the greater the risk.

    Jack M


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •