    Default Garage Fire Separation From House

    Hi:

    Code says that required fire separation from house and garage must be 1/2" drywall or equivalent.

    Is OSB panels equivalent?

    House built in 1999.

    Thanks,
    Joe

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Joe Arcaro; 01-26-2011 at 02:29 PM.
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Garage Fire Separation From House

    Quote Originally Posted by Joe Arcaro View Post
    Hi:

    Code says that required fire separation from house and garage must be 1/2" drywall or equivelant. Is OSB panels equivelant? Thanks, Joe
    No. I think plaster would be equivalent.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  3. #3
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Garage Fire Separation From House

    Presto Logs? Just kidding - Gunnar's correct.

    BTW, IMHO it was a silly change. It couldn't be that the NAHB had anything to do with it? Just asking.

    Jerry McCarthy
    Building Code/ Construction Consultant

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Garage Fire Separation From House

    Quote Originally Posted by Joe Arcaro View Post
    Code says that required fire separation from house and garage must be 1/2" drywall or equivalent.

    Is OSB panels equivalent?

    It is not "fire separation", it is simply just a "separation" wall. Throwing in the term "fire" implies that it may be a "fire wall", which it is not.

    And, no, OSB is not equivalent ... unless the OSB was FRT, in which case someone would need to certify that it was equivalent. Could you have OSB backing on the wall and gypsum board over it? Sure.

    The IRC skirts around the "fire" separation issue by simply calling it a "separation" wall, yet, when cables, conduit, pipes, etc., penetrate through that "separation" wall, those items "shall be protected by filling the opening around the penetrating item with approved material to resist the free passage of flame and products of combustion", which implies the are dancing around the term "fire" quite closely.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: Garage Fire Separation From House

    Is the OSB fire rated????? Could not see any stamps in picture.
    Drywall has a fire rating, as is sheet metal, brick, etc.


  6. #6
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Garage Fire Separation From House

    Are these SIPs?


  7. #7
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Garage Fire Separation From House

    I agree with EC Jerry about the so called "fire separation" designation. However, the California Residential Code and IRC do not.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jerry McCarthy
    Building Code/ Construction Consultant

  8. #8
    Thomas Randall's Avatar
    Thomas Randall Guest

    Default Re: Garage Fire Separation From House

    When did fire separation walls begin to be required and would plaster in a 1965 house count as fire separation or just separation?


  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Garage Fire Separation From House

    Quote Originally Posted by Thomas Randall View Post
    When did fire separation walls begin to be required ...
    There were many different variations of the garage/carport "separation" walls in the past, and many existed at the same time. Some were referred to a "fire" separation walls using various terms, but few (if any) were true "fire-resistance rated" walls which actually were constructed to any fire-resistance rated wall design, most were nothing more than an assembly of components used in fire-resistance rated wall construction. For example, the garage side was required to be Type X drywall on the garage side, but not on the house side, and the electrical membrane penetrations were sometimes required to be protected (but most of the time were not so required).

    The simple answer is that this "separation" wall when through a lot of growing pains as different people tried to understand and describe the actual purpose of the wall. What we have today is that most acknowledge that this wall is simply a "separation" wall and is not a "fire-resistance rated" wall.

    ... and would plaster in a 1965 house count as fire separation or just separation?
    In some AHJ, yes, in other AHJ, maybe not.

    Question, is the plaster on the garage side too, or just the house side? The key is what is on the house side, and what openings are in that wall (including any doors or windows, ductwork, etc.).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Thomas Randall's Avatar
    Thomas Randall Guest

    Default Re: Garage Fire Separation From House

    Jerry, thank you for your input.


    The plaster is garage side. It appears to be a skim coat over a drywall backing. On the house side there is drywall but also open framing in one small area behind some stairs (split entry home).

    There are penetrations that have been filled with expanding foam (I will be calling for something more appropriate and the door to the living space is more than inadequate (hollow core, not self closing).

    It seems I should make my references to the 'Separation Wall' and not to a fire rated one.


  11. #11
    Join Date
    Aug 2009
    Location
    Michigan
    Posts
    249

    Default Re: Garage Fire Separation From House

    I think the reason it's call a separation wall instead of a firewall is because a firewall requires a design and should be UL rated. A design should be done by a qualified designer, not a contrator. Most residential construction does not require sealed drawings. My opinion is that it's the codes way of getting some protection without the wall needing design and testing. Any other opinions?

    Randy Gordon, construction
    Michigan Building Inspector/Plan Reviewer

  12. #12
    Join Date
    Apr 2009
    Location
    Carbondale, IL
    Posts
    8

    Default Re: Garage Fire Separation From House

    Quote Originally Posted by Jerry Peck View Post
    Could you have OSB backing on the wall and gypsum board over it? Sure.
    What about OSB over drywall?


  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Garage Fire Separation From House

    Quote Originally Posted by David Miller View Post
    What about OSB over drywall?
    Nothing says you can't try to burn your house down another way if one way is not allowed ...

    If the OSB catches on fire, the 1/2 gypsum is still there to protect the separation for the same amount of time as it would have before.

    Just like when installing "fireblocking" ... wood is used for that purpose, 2x wood, 2 layers of 1x wood with the joints offset, 1/2" gypsum, 3/4" plywood with 3/4" plywood over any joints, etc.

    The 1/2" OSB would actually help delay the fire from burning through the separation wall, but ... when the OSB becomes fully on fire, that would be a detriment, hopefully, however, the people has had time, even more time, to escape.

    I was having a conversation about EEROs with someone and realized that not only does EERO stand for Emergency Escape and Rescue Opening, but it also stands for Emergency Escape or Recovery Opening as it could be used for that purpose too ... although Emergency Escape and Rescue has a much better sound to it ...

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •