Results 1 to 6 of 6
  1. #1
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Electrical Panel

    Very unusual to see a 200 amp box with service wiring rated for a 100 amp service. (Correct) How is this panel working and the unprotected wires on the main lug. Comments Please

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Electrical Panel

    It looks like they needed more circuit spaces than a 100 amp panel had space for.

    Is there a properly sized disconnect ahead of this panel?

    The small conductors in the main lugs are incorrect.


  3. #3
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Electrical Panel

    Is that discoloration/heat/scorch below the main disconnect?


  4. #4
    Join Date
    Mar 2007
    Location
    Western Montana
    Posts
    261

    Default Re: Electrical Panel

    I see some variation of this fairly often, usually when someone is doing an addition and adding a sub panel, or similar. In many cases the panel enclosure comes with the 200-amp breaker as part of the package. So the homeowner or apprentice electrician doesn't bother to change out the main breaker even though the gauge of the service feed is too small.

    The previous question is pertinent,
    "Is there a properly sized disconnect ahead of this panel?"
    It doesn't necessarily make it correct, but if for example this is a sub panel, and there is a main panel upstream that contains the proper sized disconnect for this wires feeding this panel, then protection is provided. In that case I just make sure that the homeowner knows that the true capacity of this panel is only rated for 100-amps, and recommend replacement as a precaution.

    The state inspector in my area is pretty loose on some code specifics as long as it doesn't pose a hazard (if anyone bothers to apply for a permit, which is seldom).


  5. #5
    Join Date
    Nov 2010
    Location
    California
    Posts
    97

    Default Re: Electrical Panel

    It is hard to tell from the picture but it appears that several white conductors land on circuit breakers. I do see a small gauge wire that is black with a portion wrapped with white tape to identify it as a neutral and a small gauge wire installed at the main lugs.
    None of that is permitted and suggests that whoever did the work didn't know what they were doing.


  6. #6
    Join Date
    May 2008
    Location
    N. Syracuse, NY
    Posts
    36

    Default Re: Electrical Panel

    #1: it's not a main lug panel, indicating it's probably service equipment. #2: there's no isolated neutral bar and the grounds are not seperated, again indicating service equipment. #3: it's a 40 space panel, inviting potential overload. #4: there's no overcurrent protection on those little wires in the lugs.
    #5: the 100 amp wire (maybe even 60 amp?) feeding that panel is undersized.
    #6: the white wires in the breakers need to be marked.

    Last edited by Mike Locurcio; 02-18-2011 at 07:35 AM.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •