    Default Cat IV in bedroom closet

    Today's inspection had a newer Cat IV furnace in a bedroom closet with a louvered bifold door. All of the combustion air was drawn from outside. Is this allowed?

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Cat IV in bedroom closet

    That's a little more of a tricky question. Don't know what Code you are under or if your municipality has specific requirements.
    Outside as in exterior combustion air pipe? If Yes then that would be one plus mark. Other things to consider in terms of whether the unit and location are compliant or not.
    - local fire separation requirements, is this SF or multi unit Condo; 5/8" or 1/2" drywall, type of door etc.
    - furnace set on non-combustible floor surface
    - proper drain line for condensate
    - where is main return being pulled from
    - is it a sealed box unit or open box unit
    - is the a smoke and CM detector
    - orientation of supply and return registers for the room if any
    - drain pan for furnace, some muni require it if unit is in upper level
    - does there a gap at the bottom of the room door
    Not trying to make it complicated, just looking to ask all the question in order to protect the client.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  3. #3
    Join Date
    Oct 2010
    Location
    Southwest US
    Posts
    585

    Default Re: Cat IV in bedroom closet

    Quote Originally Posted by Markus Keller View Post
    That's a little more of a tricky question. Don't know what Code you are under or if your municipality has specific requirements.
    Outside as in exterior combustion air pipe? If Yes then that would be one plus mark. Other things to consider in terms of whether the unit and location are compliant or not.
    - local fire separation requirements, is this SF or multi unit Condo; 5/8" or 1/2" drywall, type of door etc.
    - furnace set on non-combustible floor surface
    - proper drain line for condensate
    - where is main return being pulled from
    - is it a sealed box unit or open box unit
    - is the a smoke and CM detector
    - orientation of supply and return registers for the room if any
    - drain pan for furnace, some muni require it if unit is in upper level
    - does there a gap at the bottom of the room door
    Not trying to make it complicated, just looking to ask all the question in order to protect the client.
    Thanks Marcus,
    Single family home
    On concrete floor in a walk-out basement bedroom
    Condensate pump
    Return is upstairs
    1 supply register in the room about 6 feet from the closet door
    Sealed unit, Supply air piped from the exterior
    Smoke detectors but no CO detector seen
    The door is louvered (may as well not be a door)

    Last edited by Benjamin Thompson; 02-07-2011 at 04:40 PM.

  4. #4
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Cat IV in bedroom closet

    I would check the manufactures installation instructions for approved or prohibited locations.


  5. #5
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Cat IV in bedroom closet

    Sealed units have problems like any other gas fired unit. If it is in a bedroom closet and it is open to the bedroom I would say no. Leaks, defects etc, just to many things that can go wrong and then the bedroom occupant dies in their sleep.

    No, I have not looked it up yet but the gut says no for any reason or number of reasons.


  6. #6
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Cat IV in bedroom closet

    Quote Originally Posted by Benjamin Thompson View Post
    Today's inspection had a newer Cat IV furnace in a bedroom closet with a louvered bifold door. All of the combustion air was drawn from outside. Is this allowed?
    In my area if the door was solid and sealed with weather stripping it would be OK.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  7. #7
    Join Date
    Oct 2010
    Location
    Southwest US
    Posts
    585

    Default Re: Cat IV in bedroom closet

    Quote Originally Posted by Scott Patterson View Post
    In my area if the door was solid and sealed with weather stripping it would be OK.
    That's exactly what I recommended along with the door being self-closing. I just wonder why this was passed by the city 2 years ago.


  8. #8
    Join Date
    Mar 2007
    Location
    Succasunna NJ
    Posts
    577

    Default Re: Cat IV in bedroom closet

    Combustion air shall not be obtained from a sleeping room.

    Exception- Appliances installed in an enclosure in which all combustion air is taken from the outdoors and the enclosure is equipped with a solid weather-stripped door and self-closing device.

    Darren www.aboutthehouseinspections.com