    hey all

    found this today on 1921 year old house. drain directly off garbage disposal--only one drain. can potatoe peels swim up hill ??? this is wrong yes

    cvf

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: disposal and sink drain uphill

    senior moment again--they are coming faster theses days

    pictures

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  3. #3
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by CHARLIE VAN FLEET View Post
    senior moment again--they are coming faster theses days

    pictures
    I guess the dishwasher pump is helping out a bit. We sure see some funny stuff.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  4. #4
    Join Date
    Jul 2007
    Location
    Chicago
    Posts
    928

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by John Kogel View Post
    I guess the dishwasher pump is helping out a bit. We sure see some funny stuff.
    1/4' rule holds for lots of components including 1 1/2 " drain pipe.
    Not thrilled seeing the dishwasher attached to the disposal either.Some areas require a air gap and I like to see that hose all the way up to prevent any chance of contamination to the dishwasher.


  5. #5
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Bob Elliott View Post
    1/4' rule holds for lots of components including 1 1/2 " drain pipe.
    Not thrilled seeing the dishwasher attached to the disposal either.Some areas require a air gap and I like to see that hose all the way up to prevent any chance of contamination to the dishwasher.
    That dishwasher hookup is pretty standard around here.

    "It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey

  6. #6
    Join Date
    Jul 2007
    Location
    Chicago
    Posts
    928

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Nick Ostrowski View Post
    That dishwasher hookup is pretty standard around here.
    Yeah ,may depend on area.
    Here is what I use in reports.

    Airgaps are now standard equipment to assure a separation between supply and waste water. It is advised that either an airgap or a high loop be installed between the dishwasher and the waste connection.

    I think in Chicago the disposal hook up is not really allowed as if the drain gets plugged the water can be forced into the dishwasher with no gap.

    If I see it is hooked to a disposal I would defiantly be recommending air gap as needed though it never gets enforced around here .


  7. #7
    Widdershins Saunders's Avatar
    Widdershins Saunders Guest

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by CHARLIE VAN FLEET View Post
    hey all

    found this today on 1921 year old house. drain directly off garbage disposal--only one drain. can potatoe peels swim up hill ??? this is wrong yes

    cvf
    That's disgusting,

    It probably would have taken less than two hours to cut out the back of that cabinet. lower the drain and install a new cabinet back.

    That chrome offset probably cost them twice what the materials to do this right would have cost.

    And the lack of an air gap definitely wouldn't fly in my neck of the woods.


  8. #8
    Join Date
    Mar 2007
    Location
    Oregon
    Posts
    2,365

    Default Re: disposal and sink drain uphill

    Along with the other backwards things out here in Oregon, air gaps aren't standard..... high-loops for the drain hoses are the intended installation. At least it leaves a nice knockout for a soap dispenser in the sink


  9. #9
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: disposal and sink drain uphill

    Prohibited (the DW connection, that is) by the IL State Plumbing code (Sec 890.710) in any case.

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  10. #10
    Widdershins Saunders's Avatar
    Widdershins Saunders Guest

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Matt Fellman View Post
    Along with the other backwards things out here in Oregon, air gaps aren't standard..... high-loops for the drain hoses are the intended installation. At least it leaves a nice knockout for a soap dispenser in the sink
    Right.

    They adopt the code -- And then they eviscerate it.

    I hold a Specialty/Residential License down there -- But I'll be damned if I'll ever work there again.


  11. #11
    Join Date
    Mar 2007
    Location
    Oregon
    Posts
    2,365

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Widdershins Saunders View Post
    Right.

    They adopt the code -- And then they eviscerate it.

    I hold a Specialty/Residential License down there -- But I'll be damned if I'll ever work there again.
    Too funny.... I was more thinking of the politics and general unorthodox nature of our state but you're exactly right about our "code" too.

    And the not working thing shouldn't be a problem.... nobody is. Our business killing policies pretty much have that locked up.


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Bob Elliott View Post
    1/4' rule holds for lots of components including 1 1/2 " drain pipe.
    Not sure what is meant by that?

    Do you mean it needs to be 1/4" per foot DOWNHILL, or that 1/4" per foot UPHILL is okay as long as it is 1/4" per foot?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Mar 2007
    Location
    Oregon
    Posts
    2,365

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Jerry Peck View Post
    Not sure what is meant by that?

    Do you mean it needs to be 1/4" per foot DOWNHILL, or that 1/4" per foot UPHILL is okay as long as it is 1/4" per foot?
    Well, since you don't set pipes on hills I'm not sure what you mean

    Come on JP..... you REALLY don't know what he meant?


  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Matt Fellman View Post
    Come on JP..... you REALLY don't know what he meant?

    He said "1/4' rule " ... which is why I spelled it out in my question ... I have never seen a slope of " 1/4' " ... 1/4" PER FOOT yes, but not 1/4 FOOT (that's 3 inches), besides, he is not texting here, so there is no need to save characters and try to abbreviate things (or stinntscattat ) and his statement did not indicate he found anything wrong with going UPHILL (sloped uphill versus sloped downhill).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Widdershins Saunders's Avatar
    Widdershins Saunders Guest

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Matt Fellman View Post
    Well, since you don't set pipes on hills I'm not sure what you mean

    Come on JP..... you REALLY don't know what he meant?
    Jerry knew exactly what he meant, Matt, typos and all.

    Jerry just has an obsessive compulsive need to be an arsehole every once in a while.

    No big thang -- I can relate.


  16. #16
    Join Date
    Jul 2007
    Location
    Chicago
    Posts
    928

    Default Re: disposal and sink drain uphill

    Ha ha
    I sure hope a group of pro's know what I meant unless 101 speak is needed at all times.IMHO (that's text speak Jerry).
    P.S, I often do reply from my phone but some of you old geezers have no idea what that means past being grammar police.


  17. #17

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Jerry Peck View Post
    Not sure what is meant by that?

    Do you mean it needs to be 1/4" per foot DOWNHILL, or that 1/4" per foot UPHILL is okay as long as it is 1/4" per foot?
    the 1/4" rule does not apply to traps, traps must be set level to maintain the proper water seal, after the trap arm enters the plumbing drainage the 1/4" pitch must be maintained


  18. #18
    Join Date
    Jan 2011
    Location
    Utah
    Posts
    112

    Default Re: disposal and sink drain uphill

    I think a "Potatoe" is a fungus. But on the other hand, potato peels and the other food waste will be forced up the extended trap, due to the water mix. However, water will always stand in the disposer. Actually, the inch or so of water standing in the disposer, will provide the hydraulic force to push the food up the ramp. Another example of back-yard plumbing.


  19. #19
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Richard D'Aquanno View Post
    the 1/4" rule does not apply to traps, traps must be set level to maintain the proper water seal, after the trap arm enters the plumbing drainage the 1/4" pitch must be maintained
    Thanks, Richard. you are correct that air must be able to flow back along the trap arm from the vertical stack. So the top of the trap arm pipe at its drain end must be above the bottom of the pipe at the trap end. Keeping it level would achieve that regardless of the length of the arm.

    OK so which is it? Who says it needs to be level and who says it needs to be nearly level?

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  20. #20
    Widdershins Saunders's Avatar
    Widdershins Saunders Guest

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by John Kogel View Post
    Thanks, Richard. you are correct that air must be able to flow back along the trap arm from the vertical stack. So the top of the trap arm pipe at its drain end must be above the bottom of the pipe at the trap end. Keeping it level would achieve that regardless of the length of the arm.

    OK so which is it? Who says it needs to be level and who says it needs to be nearly level?
    As a Plumber, the portion of the trap arm that I stub into the sink box has just enough grade to barely register on my torpedo level -- Likely just a 1/16 of an inch per foot.

    Tubular plastic p-traps can be 'trained' to flex a little, but schedule 40 plastic union or tubular brass traps can be very unforgiving.


  21. #21
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Richard D'Aquanno View Post
    the 1/4" rule does not apply to traps, traps must be set level to maintain the proper water seal, after the trap arm enters the plumbing drainage the 1/4" pitch must be maintained
    Of course 'the trap' must be level, and, of course 'the trap arm' must not be level, the trap arm must slope DOWN to the vent.

    Not sure where you got anything about 'the trap' not being level.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  22. #22
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by John Kogel View Post
    Thanks, Richard. you are correct that air must be able to flow back along the trap arm from the vertical stack. So the top of the trap arm pipe at its drain end must be above the bottom of the pipe at the trap end. Keeping it level would achieve that regardless of the length of the arm.

    OK so which is it? Who says it needs to be level and who says it needs to be nearly level?
    It is 'not allowed' to be level, it is 'required' to be sloped.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  23. #23

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Jerry Peck View Post
    It is 'not allowed' to be level, it is 'required' to be sloped.
    national standard plumbing code 5.3.3 traps MUST be level


    5.3.3 Trap Setting and Protection
    Traps shall be set level with respect to their water seals and, where necessary, shall be protected from freez- ing.


    funny thing is, for the last 20 years the code states the same info

    but to get back on subject the picture shows the installation in wrong and need to be changed


  24. #24
    Widdershins Saunders's Avatar
    Widdershins Saunders Guest

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Jerry Peck View Post
    It is 'not allowed' to be level, it is 'required' to be sloped.
    And most of the folks forced into putting your nugget of wisdom into practical use will tell you to get bent, Jerry.

    Seriously -- Walk a mile in the shoes of the folks you're foisting your limited, book learned knowledge upon before pontificating.

    And while you're at it, take a few moments to edify yourself on the limiting factors of the products we're forced to deal with.

    Prick.


  25. #25
    Join Date
    Jul 2007
    Location
    Chicago
    Posts
    928

    Default Re: disposal and sink drain uphill

    Busy with all NACHI video going free to members,New beta version of Home Inspector Pro,and a new domain,plus work however to explain my original remark I was not being literal to the trap but to plumbing drains in general not to mention flue slope and deck slope.
    The quarter inch rule seems to apply in many aspects of systems and components.
    Seems every time I post a self installed guardian of code goes off the handle.
    I use code to back up my opinion but no one better pretend to be a code Inspector in the report or they will lose in court big time.
    Anyway ,just thought I would explain my earlier post after the "hot heads" cooled off.
    Have a great weekend inspecting to all.


  26. #26
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Richard D'Aquanno View Post
    national standard plumbing code 5.3.3 traps MUST be level


    5.3.3 Trap Setting and Protection
    Traps shall be set level with respect to their water seals and, where necessary, shall be protected from freez- ing.


    funny thing is, for the last 20 years the code states the same info

    but to get back on subject the picture shows the installation in wrong and need to be changed
    Richard,

    Are you simply NOT READING what I am writing ... or are you just ignoring what I wrote and you read?

    (bold red is my highlighting to help you read what I wrote)
    Quote Originally Posted by Jerry Peck View Post
    Of course 'the trap' must be level, and, of course 'the trap arm' must not be level, the trap arm must slope DOWN to the vent.

    Not sure where you got anything about 'the trap' not being level.
    Yet ANOTHER ONE who CANNOT READ (or simply chooses to not read) what is written:
    Quote Originally Posted by Widdershins Saunders View Post
    And most of the folks forced into putting your nugget of wisdom into practical use will tell you to get bent, Jerry.

    Seriously -- Walk a mile in the shoes of the folks you're foisting your limited, book learned knowledge upon before pontificating.

    And while you're at it, take a few moments to edify yourself on the limiting factors of the products we're forced to deal with.

    Prick.
    Or, maybe they can actually read, maybe they just do not understand the difference between a "trap" and the "trap arm"?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  27. #27

    Default Re: disposal and sink drain uphill

    no i did read it, and yes the trap arm can extend into the wall to the vent
    i am looking at what is visible under the sink and the trap arm is part of the trap

    not trying to bash anyone here, if i see something that involves my trade i try to post on it


  28. #28
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Richard D'Aquanno View Post
    no i did read it, and yes the trap arm can extend into the wall to the vent
    Richard,

    Again, based on your response, you are not *reading* what is written - you are applying what you want it to say before *reading* and and then responding to what you want it to say.

    NO WHERE in there as anyone, least of all me, said that a trap arm cannot extend into the wall to the vent ... what is being said, and which you are either not reading or ignoring is that THE TRAP ARM ... THE ... TRAP ... ARM ... is required to be sloped down from the trap to the vent.

    Repeat that ... THE TRAP ARM ... not 'the trap' and and not anything else ...

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  29. #29
    Widdershins Saunders's Avatar
    Widdershins Saunders Guest

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Jerry Peck View Post
    Richard,

    Again, based on your response, you are not *reading* what is written - you are applying what you want it to say before *reading* and and then responding to what you want it to say.

    NO WHERE in there as anyone, least of all me, said that a trap arm cannot extend into the wall to the vent ... what is being said, and which you are either not reading or ignoring is that THE TRAP ARM ... THE ... TRAP ... ARM ... is required to be sloped down from the trap to the vent.

    Repeat that ... THE TRAP ARM ... not 'the trap' and and not anything else ...
    *chuckles*

    You're such an ass, Jerry.

    Is it any wonder that a few of your Peers say they wouldn't piss on you if you were on fire?

    And that's a direct quote from two of your Peers in Ormond Beach -- Most of the other quotes regarding you from your local Peers aren't clean enough to post in this forum.


  30. #30

    Default Re: disposal and sink drain uphill

    Quote Originally Posted by Jerry Peck View Post
    Richard,

    Again, based on your response, you are not *reading* what is written - you are applying what you want it to say before *reading* and and then responding to what you want it to say.

    NO WHERE in there as anyone, least of all me, said that a trap arm cannot extend into the wall to the vent ... what is being said, and which you are either not reading or ignoring is that THE TRAP ARM ... THE ... TRAP ... ARM ... is required to be sloped down from the trap to the vent.

    Repeat that ... THE TRAP ARM ... not 'the trap' and and not anything else ...
    again, you,re not listening, think about it first and picture the trap, from the "u"bend ….trap weir to the wall is considered the trap arm and that is the only part i am talking about. do we know where the vent is …no, it could be directly behind the wall or 5' away, we are looking at, and talking about the visible trap and trap arm in the picture


  31. #31
    Join Date
    Nov 2010
    Location
    CO
    Posts
    48

    Default Re: disposal and sink drain uphill

    I’m curious, how long has that been in the current configuration and does it drain?


  32. #32
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: disposal and sink drain uphill

    jeff

    not sure why that is relevant. it is draining up hill. would you write it up ??

    what happens when it doesn't ??

    code says 1/4 " slope per foot--downward.

    cvf


  33. #33
    Join Date
    Nov 2010
    Location
    CO
    Posts
    48

    Default Re: disposal and sink drain uphill

    Not sure it is relevant, just curious.
    Yes I would put it in the report.
    and if it stopped draining, call the plumber.


  34. #34
    Join Date
    Jun 2010
    Location
    Vancouver
    Posts
    202

    Default Re: disposal and sink drain uphill

    Hey Jeff, I think it is draining based on the fact it is still there. the water is coming from higher up and is going to a lower level. just not right away for all of it. the water is going to rise up high enough to drain just not all of it and properly. the garbage disposal will push some of it out too. but the loop will hold a lot back from draining properly. And yes by all means write it up.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •