Results 1 to 14 of 14
Thread: Wye Fittings
    Iron Mountain, MI
    Default Wye Fittings
    Hi:
    The attached photo shows wye fittings installed horizontallly on a main waste pipe. Are horizontal wyes ok? The vertical pipes come from the kitchen and bathroom sinks. The main drain exits to the right to a septic tank.
    Also curious about the oversized main drain (4"). Anything wrong with that?
    Thanks,
    Joe
    Apr 2007
    WESTMINSTER CO
    Default Re: Wye Fittings
    waste drain should have a 1/4 " slope downward to keep solids and liquid from lying on bottom of pipe--see photo
    cvf
    Here is what the NC Plumbing Code says about a change of direction.
    Attached Files Attached Files
    The IRC allows wye for changes in direction from: horizontal to vertical, vertical to horizontal, and horizontal to horizontal.
    That looks like it might be being used as a cleanout?
    Iron Mountain, MI
    Hi Jerry:
    Actually I'm talking the fittings to the left and right of the wye cleanout. What are these fittings called?
    Iron Mountain, MI
    Hi James:
    So according to the chart, this configuration is ok. Correct?
    Not really I don't think. You have two sanitary T's going from vertical to horizontal and that is not approved in NC. You might want to use a combination y and eighth bend.
    Quote Originally Posted by Joe Arcaro View Post
    Hi Jerry:
    Joe,
    Those are sanitary tees, and sanitary tees are approved for changes in direction from horizontal to vertical only.
    Your photos shows those sanitary tees installed changing direction from vertical to horizontal - not allowed.
    As James said, a combination wye and eight bend could be used there.
    May 2010
    No. San Diego Co., CA
    Doesn't make much sense to me to put a Wye for a clean-out there in the first place. Why not install a clean-out and plug the to the left of the kitchen waste? Or, if that's not the beginning of the run, put a Wye for clean-out there before the two vertical waste lines.
    ip
    Wye's are fine IF installed with the branch coming in above the flow line.
    The flow line is considered the bottom 1/3 of the pipe. So H to H is okay if you "roll" the fitting and add a street 1/16 bend to get back level on the branch.
    No "flat" plumbing allowed.
    877-466-8504
    I agree, but ... I could not think of another reason for that wye to be there ... can you?
    Hi:
    Thanks,
    Joe
    Now that I look at the pic again, the San-T's are not allowed "on their back" as installed. 45 degree max incline or change to a combination.
    Over sized drains are often used in "flat plumbed" combination waste and vent system like those used in markets etc for floor sinks that are not near a wall for venting. The additional air space above the effluent is used for venting.
    877-466-8504
    Drain lines are sized to be self-scouring. The problem with over-sized drain lines is that the water will drain leaving the solids behind in the pipe. The code also says that the lowest horizontal sewer has to be 4" in residential so this 4" is not over sized....IMO
    May 2010
    Jerry
    Looking at the set-up, (the 90 bend on the 1/2" copper on the right also looks crimped to me), I'll give a qualified plumber the benefit of the doubt and say it was a home-owner's DIY attempt. Possibly, if the block wall's return was too tight then maybe there was insufficient room for any meaningful clean-out to the left of the wastes but that could/should have been addressed by better design and planning. Appropriate combos would have provided necessary clearance and significantly less likelyhood of a blockage.
    ip
