    The connections don't look right to me. All the wiring is under the screws of the breakers but it looks like they should be inserted between two plates and the screw tightening down on it to make a pressure connection. I think the picture shows that some of the wiring is only barely under the screw. The metal plates may not be visible though. The panel was a Commander.
    Thanks

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    James Duffin's Avatar
    James Duffin Guest

    Default Re: conductor under screw of the breaker

    Is that a 90 amp breaker with either #10 or #8 going to it? I agree with you that the way the wires are attached to the breakers looks wrong.


  3. #3
    Bert de Haan's Avatar
    Bert de Haan Guest

    Default Re: conductor under screw of the breaker

    # 8 on a 40 amp. Thanks for your comment


  4. #4
    Bob Jack's Avatar
    Bob Jack Guest

    Default Re: conductor under screw of the breaker

    I agree with you on the conductor placement under the screw. The electrician did noot take the time to look at what they were doing. For proper tension to be applied to the conductor it should be in the sadle of the conductor scoket.