Results 1 to 27 of 27

Thread: Heat Pump

  1. #1
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Heat Pump

    I've never seen an air-source heat-pump here in Chicago, just ground-source systems.

    However, this afternoon I ran into the arrangement below -and I've not sure exactly what I'm seeing:

    Exterior unit was built by York, the capacity plate was weathered and completely illegible.

    At the interior there was a conventional GFAF.

    The coil above it is listed for cooling use only.

    On the wall next to the furnace was a controller marked: "Accessory For Heat Pump", connected to the furnace as shown (brown wire to left in 6th picture).

    In the blower compartment, connected to the blower, there was a relay, as shown.

    What am I looking at here?

    Thanks as always.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  2. #2
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Heat Pump

    It would help to know what wires were on the thermostat if you have that info available.


  3. #3
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Heat Pump

    Sorry, in retrospect I realized that the T-Stat is likely an important piece of the puzzle, but as best I remember it it was a conventional programmable heating/cooling unit, I did not notice an "emergency heat setting".

    (Part of the problem is that I have never seen an air-source heat pump here - the climate is too cold - so I have no experience with operating or inspecting them other that what I have encountered in casual reading).

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  4. #4
    mitch buchanan's Avatar
    mitch buchanan Guest

    Default Re: Heat Pump

    Michael,

    One easy way to identify an air source heat pump is to look for the reversing valve inside the condenser next to the compressor. Sorry I don't have a picture, but it's a small "box" in-line with the vapor and suction lines. I'm sure others have a better explaination, but when I can't tell from looking at the thermostat, I look for the reversing valve. Hope this helps!


  5. #5
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Heat Pump

    The best I can tell that box on the wall is the dual-fuel kit for a heat pump. Here is a link to a similar item:

    http://www.hamiltonhomeproducts.com/...il-Fue-Kit.pdf


  6. #6
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Heat Pump

    Quote Originally Posted by mitch buchanan View Post
    One easy way to identify an air source heat pump is to look for the reversing valve inside the condenser next to the compressor. Sorry I don't have a picture, but it's a small "box" in-line with the vapor and suction lines. I'm sure others have a better explaination, but when I can't tell from looking at the thermostat, I look for the reversing valve. Hope this helps!
    Hum... there was THIS, but at the expansion coil.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  7. #7
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: Heat Pump

    An air source heat pump in Chicago doesn't sound like the best heating option for a house.

    "It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey

  8. #8
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Heat Pump

    Quote Originally Posted by Nick Ostrowski View Post
    An air source heat pump in Chicago doesn't sound like the best heating option for a house.
    As I said, if there is a air-source heat pump as a component of this system, it will be a first for me.

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  9. #9
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Heat Pump

    From what you described it sounds like a dual fuel heat pump system with a gas furnace as the backup heat rather than electric heat strips. How hot was the air leaving the registers in heat pump mode (if it wasn't too cold for the heat pump to be running).


  10. #10
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Heat Pump

    Michael, you have pic's of data plates that state: "80,000 btu natural gas", and another that states: "cooling air conditioner".

    What makes you think it is a heat pump?

    The beatings will continue until morale has improved. mgt.

  11. #11
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Heat Pump

    Quote Originally Posted by Vern Heiler View Post
    Michael, you have pic's of data plates that state: "80,000 btu natural gas", and another that states: "cooling air conditioner".

    What makes you think it is a heat pump?
    The presence of the heat pump controller in the 5th picture, and its connection to the furnace.

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  12. #12
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Heat Pump

    Quote Originally Posted by Michael Thomas View Post
    The presence of the heat pump controller in the 5th picture, and its connection to the furnace.
    Remnants of an old and long gone system!

    The indoor coil of a heat pump has to be able to handle the condensing pressures. The label states for cooling only! Can't be used as a heat pump indoor coil.

    The beatings will continue until morale has improved. mgt.

  13. #13
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Heat Pump

    Quote Originally Posted by Vern Heiler View Post
    Remnants of an old and long gone system!

    The indoor coil of a heat pump has to be able to handle the condensing pressures. The label states for cooling only! Can't be used as a heat pump indoor coil.
    Vern,

    The controller is connected to the existing furnace, which appears to be original to the townhome.

    Confusing, I know....

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  14. #14
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Heat Pump

    I can't explane the controller, or what ever it is, as I have never seen one like it. But I can tell you that the coil that is marked "cooling only" can't be used as a heat pump. You also have to have a transfer valve at the outdoor unit.

    The beatings will continue until morale has improved. mgt.

  15. #15
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Heat Pump

    I'm with Vern on this, even if it was an exterior heat pump, looks like they replaced it with a cooling coil to keep the a/c functioning. Need to know if the outdoor unit was in fact a heat pump still from either the data plate or look for the reversing valve. If I saw no method of operating the heat pump then I would just punt it to and a/c tech mentioning "mismatched parts and pieces from incompatible systems" and let them figure it out. Obviously it was too cold to test the A/C so your kind of at a loss anyway.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  16. #16
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Heat Pump

    Thanks for the comments.

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  17. #17
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Heat Pump

    Quote Originally Posted by Michael Thomas View Post
    As I said, if there is a air-source heat pump as a component of this system, it will be a first for me.
    I don't know how cold it gets and stays in your area but there are heat pumps that are efficient down to -13 degrees. I use my conventional heat pump down to 20 degrees and it is more efficient than my gas backup furnace.


  18. #18
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Heat Pump

    Michael, I just looked at the link James posted regarding the "heat pump add-on". That is the old technology. New thermostats are available that take the place of the extra panel and wiring, making dual fuel systems much more affordable.

    You may have more dual fuel systems than you know! Sometimes it is hard to tell during an inspection. The thermostats do not look any different than single fuel thermostats. Here are a few things I look for: (1) the word "Heat Pump" on the outdoor unit, that one is a give-me, (2) three service test points instead of two at the outdoor unit, (3) reversing valve viewed at the outdoor unit, sometimes hard to see, Trane hides them behind the cover. (4) thermostat set for heat, and the furnace does not ignite, check to see if the outdoor unit started instead.

    If you find that a system is a "dual fuel system" you should advise the customer to verify the thermostat is configured correctly. If it is not setup for duel fuel heat pump, the compressor can run at the same time as the furnace. Not good for the heat pump. If the manual is available I tell them they can check the settings, but suggest having a qualified HVAC contractor do it during the next maintenance.

    The beatings will continue until morale has improved. mgt.

  19. #19
    David Bell's Avatar
    David Bell Guest

    Default Re: Heat Pump

    Furnace , coil and humidifier look new. My guess is they tried to save some bucks by re-using the heat pump as a straight cooling condenser. The hawkeye in the blower compartment is most likely for the humidifier so it will only operate if the blower is going. The remaining accessory box may still be used to operate the heat pump/condenser as it may have a cool active reversing valve that needs to be powered for cooling.


  20. #20
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Heat Pump

    I don't think that's a heat pump system. I think the controller was put in for some reason and is confusing the appearance. Based on what I'm seeing and the label plates looks like standard heat/ac. The controller may have been put in to run the blower motor for air circulation during moderate weather.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  21. #21
    Join Date
    Jul 2008
    Location
    Utah
    Posts
    390

    Default Re: Heat Pump

    Quote Originally Posted by James Duffin View Post
    I don't know how cold it gets and stays in your area but there are heat pumps that are efficient down to -13 degrees. I use my conventional heat pump down to 20 degrees and it is more efficient than my gas backup furnace.
    Heat pump more efficient than gas furnace? Of course, but it isn't less costly to operate than a gas furnace. At least in my neck of the woods.


  22. #22
    Join Date
    Aug 2008
    Location
    Pleasant Hill, Iowa
    Posts
    145

    Default Re: Heat Pump

    Looks to me that they installed a furnace and a-coil and used the old heat pump as a condenser. You have a gas furnace with DX cooling! pic 7 is a current sensing relay for the humidifier, and pic 6 is a transformer/fan relay. Also note in pic #2 The furnace and water heater vent connectors are installed wrong, they are to go into the side of a B-Vent "T" and not up into the bottom of the B-Vent. FYI

    Dan Hagman ACI
    ProSite Home Inspections
    Des Moines, Iowa

  23. #23
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Heat Pump

    Quote Originally Posted by Dan Hagman View Post
    Also note in pic #2 The furnace and water heater vent connectors are installed wrong, they are to go into the side of a B-Vent "T" and not up into the bottom of the B-Vent. FYI
    Dan, can you expand on this? All of the diagrams I have found in the 1993 NC Gas Code (I know its old!), show the first appliance into the bottom, with the rest of the connections into the side of a "T". I couldn't find anything that prohibited the use of a "Y" though.

    The beatings will continue until morale has improved. mgt.

  24. #24
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Heat Pump

    Quote Originally Posted by Rod Butler View Post
    Heat pump more efficient than gas furnace? Of course, but it isn't less costly to operate than a gas furnace. At least in my neck of the woods.
    It is if you gas is propane. The cost per BTU using the heat pump is about 1/3 the cost of propane. What is the cost of gas and electricity in your area?


  25. #25
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Heat Pump

    Quote Originally Posted by Dan Hagman View Post
    Looks to me that they installed a furnace and a-coil and used the old heat pump as a condenser. You have a gas furnace with DX cooling! pic 7 is a current sensing relay for the humidifier, and pic 6 is a transformer/fan relay. Also note in pic #2 The furnace and water heater vent connectors are installed wrong, they are to go into the side of a B-Vent "T" and not up into the bottom of the B-Vent. FYI
    Since we are guessing...I guess they put a heat pump coil in an old coil box.


  26. #26
    Join Date
    Aug 2008
    Location
    Pleasant Hill, Iowa
    Posts
    145

    Default Re: Heat Pump

    Quote Originally Posted by Vern Heiler View Post
    Dan, can you expand on this? All of the diagrams I have found in the 1993 NC Gas Code (I know its old!), show the first appliance into the bottom, with the rest of the connections into the side of a "T". I couldn't find anything that prohibited the use of a "Y" though.
    Vern, I hear what you are saying! I see the same thing also, but, I have replaced too many rusted out vent connectors on water heaters and inducer motors on 80% efficent furnaces that were installed into the bottom of the B-Vent. What happens alot, is the furnaces are replaced with a 90% + and the water heater vent connector is left in the bottom of an oversized B-Vent. On a 2-story house the water heater flu gas does not stay hot enough all the way to the top and condensation forms on the inside of the B-Vent and runs down and into the single wall vent connector and rusts it out and then you have a possible CO leak. If the vent connector goes into the side of the B-Vent there is no way the condensation will rust out the single wall vent connector or the inducer motor on the furnace. The condensation goes to the bottom of the "T" cap and evaporates. A properly sized B-Vent will not have this problem. The local inspectors would alway require this installation to be done. I can't find it either in the UMC or the National Fuel Gas Code or the IRC but think of it as good,better, best. I "RECOMMEND" this as an installation method, I don't say it's wrong to the customer because I can't find it in the IRC. I hope this helps with my logic. I think local jurisdiction adopted this method around here.

    Last edited by Dan Hagman; 02-28-2011 at 09:47 PM. Reason: typo
    Dan Hagman ACI
    ProSite Home Inspections
    Des Moines, Iowa

  27. #27
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Heat Pump

    MT,

    Its a york systems add-on "control" board & pwr supply interface which can house a "York Guard" demand defrost unit rather than relying on "timed defrost".

    I'm guessing (or maybe you said it already) that the coil and furnace are in a full basement and the folks get a frigid basement and are warm upstairs and like to run the AC all the time, and keep the upstairs really cold, not just in worst of summer but all "season" and even when its "too cold outside" they don't cut it off or open the windows and the york controler will prevent freeze ups on the coil inside when they're running their AC even when its below 60 outside and their still feeling "warm" and humid upstairs. Dark roof? poorly insulated? heat sinks/brick? two story or split level?

    See the wiring diagram and jumper instructions for interfacing "control unit" with gas fired FA and near bottom page 2 right column in the first pdf. I think the diagrams & references to IV is what you might find present.

    Second pdf is order sheet for a split HP similar vintage/era note bottom right column of first page ordering list of field installed accessories.

    You might try googling "york guard" and see what you find.

    HTH.

    Attached Files Attached Files
    Last edited by H.G. Watson, Sr.; 03-01-2011 at 07:46 PM.