    Default Slope of a waste line

    This is a waste line for a kitchen sink, the line is vented with a vent stack in the wall behind the sink. Is this slope excesssive, is it not to exceed 1/2 inch per foot? Or does that only apply to the trap arm

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Slope of a waste line

    This is what I found
    2006 IRC

    P3005.3 Horizontal drainage piping slope.
    Horizontal drainage
    piping shall be installed in uniform alignment at uniform
    slopes not less than
    1/4 unit vertical in 12 units horizontal
    (2-percent slope) for 2
    1/2-inch (64 mm) diameter and less, and
    not less than
    1/8 unit vertical in 12 units horizontal (1-percent

    slope) for diameters of 3 inches (76 mm) or more.


    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Slope of a waste line

    What is the difference if it has a long slope or if when it comes out of the cabinet and goes straight into the crawl to ground level and then 45s into the waste line. The slope gets pretty drastic when the waste line gets to the street connection

    Straight drop, long slope?


  4. #4
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Slope of a waste line

    Someone from the plumbing dept will correct me if I'm wrong. If the vertical angle is less than 45 degrees but more than the usual 1/4 " per foot, some sludge will be left behind.
    A pipe at 45 degrees or steeper will flush just as well as a vertical pipe.

    So that mess is the work of an amateur that never read the plumber's handbook.

    Having said all that, is there a big concern here, with crap clogging the line? Does shitt stop sliding at 44 degrees?

    Last edited by John Kogel; 03-03-2011 at 11:41 AM.
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  5. #5
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Slope of a waste line

    Quote Originally Posted by John Kogel View Post
    Someone from the plumbing dept will correct me if I'm wrong. If the vertical angle is less than 45 degrees but more than the usual 1/4 " per foot, some sludge will be left behind.
    A pipe at 45 degrees or steeper will flush just as well as a vertical pipe.

    So that mess is the work of an amateur that never read the plumber's handbook.

    Having said all that, is there a big concern here, with crap clogging the line? Does shitt stop sliding at 44 degrees?
    I guess that may depend on what the particular person ate


  6. #6
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Slope of a waste line

    1/4" per foot. The standard issue with excessive slope is that the water will outrun the solids and the solids will be left behind and eventually you'll have problems. The initial, upper run in the photo, could be a problem. The lower run is steep enough it will probably be Ok.
    My bigger concern is the sewer connections and I would recommend putting a note of concern in the report. The abandoned connection at the left side of the photos looks more like the original connection. The current ground connection looks newer, DIY, not quite kosher. From the picks I would put something in the report, further eval by plumber, camera the line, etc. Or maybe you saw enough to put comments in the report.
    Obviously the insulation and dirt concerns are already in the report.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  7. #7
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Slope of a waste line

    Thank you. This pretty much says it all. I was just a little confused about slope after reading the code book. It's like that damn thing is written in latin.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  8. #8
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Slope of a waste line

    The relief valve on the water heater is wrong in your new picture you posted unless it has a 12" sensing element on it.


  9. #9
    Join Date
    Nov 2010
    Location
    New Westminster BC
    Posts
    55

    Default Re: Slope of a waste line

    Moving slightly to the edge of this topic.... The standard reason given for the code not allowing slopes between 1 in 24 and 1 in 1 is that the water will outrun the solids it is carrying, leaving the waste behind to clog the line up. I wonder how often this happens in practice. One neighbourhood I know has streets along the contours and the slopes of many of the building sewer pipes from the houses to the street are in the disallowed range. Visual camera inspection on two such pipes (30 and 70 years old) showed no significant solid build up. Clogs that do occur are caused by roots growing into the pipes, which are then either cleaned out (a few hundred dollars every one or two years) and/or replaced (typically $2000 to $8000 one time). This happens whether or not there any suspect trees in on the property. If the house is of an age such that its underground sewer pipe is likely to be clay sections, the probability of future clogs and sewer backups due to root problems is significant and should be mentioned. In comparison the probability of clogs due to excessive slope seems remote and therefore likely should not be mentioned. Maybe it's different with smaller pipes.


  10. #10
    Join Date
    Nov 2010
    Location
    California
    Posts
    97

    Default Re: Slope of a waste line

    The 180 degree change of direction requires a clean-out. That particular no-hub fitting is not listed for plastic pipe. None of the waste pipe is supported. The water heater vent connector is not screwed to the draft hood. The water heater is located in the required clear working space in front of the electrical panel board. And what's up with the hose clamp on the copper pipe? It appears that the threaded copper fitting leaks.


  11. #11
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Slope of a waste line

    David, Cleanout, are you crazy? Do you know how much that would eat into the plumbers profit margins . This is one of the most overlooked requirements I swear. Instead of buying a 90, the poor guy has to buy a tee, female adapter and threaded plug. While were at it lets make sure any possible cleanout is located where the drywaller will definitely cover it up.
    It's unfortunate that something as simple as putting in a couple cleanouts has to be such a big deal to get a guy to do.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  12. #12
    Bill Brooks's Avatar
    Bill Brooks Guest

    Default Re: Slope of a waste line

    The reason behind the 1/4 per foot slope is they are trying to maintain the drain runs at 33% full capacity to wash out solids. Well this what we were taught in trade school in Canada. Also regarding the cleanouts by code in Canada you also have to have a cleanout every 50ft and every change of direction on the main sewer. I know I do this when roughing in homes or upgrading the plumbing but not very many plumbers do this, as stated above it cuts in to there profits or that extra few bucks may cause them to loose the job. But when I have to start cutting corners to get a job I walk away from it not worth the headaches later.


  13. #13
    Tom Thompson's Avatar
    Tom Thompson Guest

    Default Re: Slope of a waste line

    UPC requires minimal of 2%, 1/4" per foot grade on horizontal waste piping, piping greater than 45 degrees of horizontal is considered both horizontal & vertical. There are no maximum slope restrictions, but true solids will be left behind, build up will be washed out with the excessive slope. Clean out aren't required on waste lines ran greater than 72 degrees of horizontal. Plastic piping needs to be supported at no greater than 4 foot intervals. I see numerous defences and sure there are more out of viewing range. Also for dirty arms, the weir of the trap can never be above the vent take off. This restricts excessive slope from being allowed on trap arms.