Results 1 to 6 of 6
  1. #1
    brianmiller's Avatar
    brianmiller Guest

    Default ceiling fans in bathrooms

    The ceiling fan was located 12" away from the shower stall, but 8ft up from the floor. Doesn't the fan need to be 8 ft up and 3ft away?

    thanks,

    brian

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: ceiling fans in bathrooms

    Of course everything is dependent on the code that was in effect when installed.
    This is from the IRC 2006
    Bold added
    E3903.10 Bathtub and shower areas.
    Cord-connected
    luminaires, chain-, cable-, or cord-suspended-luminaires,
    lighting track, pendants, and ceiling-suspended (paddle) fans
    shall not have any parts located within a zone measured 3 feet
    (914 mm) horizontally and 8 feet (2438 mm) vertically from
    the top of a bathtub rim or shower stall threshold. This zone is
    all encompassing and includes the zone directly over the tub or
    shower. Luminaires located in this zone shall be listed for damp
    locations and where subject to shower spray, shall be listed for

    wet locations.


    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: ceiling fans in bathrooms

    Quote Originally Posted by brianmiller View Post
    The ceiling fan was located 12" away from the shower stall, but 8ft up from the floor. Doesn't the fan need to be 8 ft up and 3ft away?
    To add some clarity to the question and the answer:

    1) The closest part of the ceiling fan (tips of the blades) must be at least 3 feet horizontally from the edge of the shower stall.

    2) The lowest part of the ceiling fan (the switch housing or light kit if there is a light kit) must be at least 8 feet vertically above the top of the shower curb (including the 3 foot horizontal measurement in 1) above).

    Think of it this way: If you were to set a large box over the shower stall and rest it on the shower curb.

    The box was 8 feet high, and the box stuck out 3 feet from the edge of the shower, the ceiling fan blades (ceiling fan, pendant light, etc.) would need to clear that box.

    The ceiling fan blades could rotate 'over' that box, but if the ceiling fan blades were lower and the fan was turned on, the blades would hit that box - and that you are not be allowed to hit that box with anything.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: ceiling fans in bathrooms

    This has been posted here before.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  5. #5
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: ceiling fans in bathrooms

    Jerry,

    Did they ever get around to requiring GFCI protection on wall mounted fixtures?




    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  6. #6
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: ceiling fans in bathrooms

    Quote Originally Posted by Michael Thomas View Post
    Jerry,

    Did they ever get around to requiring GFCI protection on wall mounted fixtures?

    Unless required by the instructions there is no separate code requirement for GFI protection for the fixtures.

    All answers based on unamended National Electrical codes.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •