    Default Double Tapped - Stranded vs Solid

    Determining if a double tapped breaker terminal is accetable or not, depends only on wether or not the breaker is listed for 2 wires (i.e. SD & CH). Wether the conductor is stranded or solid does not matter (i.e. two stranded ok but two solids not...), correct?

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Double Tapped - Stranded vs Solid

    Quote Originally Posted by Andrew Kolar View Post
    Wether the conductor is stranded or solid does not matter (i.e. two stranded ok but two solids not...), correct?

    That is correct.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com