Results 1 to 21 of 21
  1. #1
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default OSB at Garage Ceiling?

    OSB at garage walls and ceilings with no gypsum board? Acceptable or not?

    Paperbacking on drywall, yes it is already noted on report.

    Opinions welcome.

    rick

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by Rick Hurst View Post
    OSB at garage walls and ceilings with no gypsum board? Acceptable or not?

    Paper backing on drywall, yes it is already noted on report.

    Opinions welcome.

    rick
    .
    Bump.

    Rick,

    As far as I got Dallas County TX currently uses ( with some exceptions) 2006 Residential Code.

    My money would be not allowed as OSB is not a fire rated material.
    .

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  3. #3
    chris mcintyre's Avatar
    chris mcintyre Guest

    Default Re: OSB at Garage Ceiling?

    Nope......at least not here. This came up a couple of weeks ago for me on a garage addition. Building inspector told me I could put the drywall on the wall between the house and garage all the way to the roof sheathing and then install the plywood/osb over the drywall (on the wall), ceiling could then be left unfinished or plywood/osb installed.


  4. #4
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: OSB at Garage Ceiling?

    Must have ceiling and common walls with gypsum board for separation.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  5. #5
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: OSB at Garage Ceiling?

    Funny how we have answers to this but Rick didn't say what's above the garage or on the other side of the walls. And no, I'm not in the habit of assuming things.

    Eric Barker, ACI
    Lake Barrington, IL

  6. #6
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: OSB at Garage Ceiling?

    Eric, only attic space above the garage and a family room opposite the front garage wall.

    Rick


  7. #7
    Join Date
    May 2007
    Location
    Tyler, TX
    Posts
    720

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by Rick Hurst View Post
    Eric, only attic space above the garage and a family room opposite the front garage wall.

    Rick
    Wall kindling. I write it up and explain it to my clients all of the time.

    Many times (many) cars are pulled into garage only to catch fire after everyone has gone into the home.

    Bruce Thompson, Lic. #9199
    www.TylerHomeInspector.com
    Home Inspections in the Tyler and East Texas area

  8. #8
    Join Date
    Nov 2010
    Location
    CO
    Posts
    48

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by Rick Hurst View Post
    OSB at garage walls and ceilings with no gypsum board? Acceptable or not?

    Paperbacking on drywall, yes it is already noted on report.

    Opinions welcome.

    rick
    Interesting question really. I think that OSB would be more of a fire resistive material than drywall, even if it was 5/8 fire stop. But the seams between the sheets, whether they are drywall or OSB, needs to be taped on the common walls and ceiling with common attic like Jim L pointed out. So the tapping is the real issue. And since nobody tapes OSB, drywall is the product to use.


    If the garage is detached from the house then it doesn't matter what you do to the walls and ceiling.



  9. #9
    Join Date
    May 2007
    Location
    Tyler, TX
    Posts
    720

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by Jeff Langhorn View Post
    Interesting question really. I think that OSB would be more of a fire resistive material than drywall, even if it was 5/8 fire stop. But the seams between the sheets, whether they are drywall or OSB, needs to be taped on the common walls and ceiling with common attic like Jim L pointed out. So the tapping is the real issue. And since nobody tapes OSB, drywall is the product to use.


    If the garage is detached from the house then it doesn't matter what you do to the walls and ceiling.
    I'm not sure why you would think OSB would be more fire resistive than gypsum, but here are some flame spread ratings for the two:

    gypsum is Class I with a flame spread of 10-15
    OSB is Class III with a flame spread of 150

    Most solid woods would be better than OSB at flame spread.

    Bruce Thompson, Lic. #9199
    www.TylerHomeInspector.com
    Home Inspections in the Tyler and East Texas area

  10. #10
    Join Date
    Nov 2010
    Location
    CO
    Posts
    48

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by Jeff Langhorn View Post
    Interesting question really. I think that OSB would be more of a fire resistive material than drywall, even if it was 5/8 fire stop. But the seams between the sheets, whether they are drywall or OSB, needs to be taped on the common walls and ceiling with common attic like Jim L pointed out. So the tapping is the real issue. And since nobody tapes OSB, drywall is the product to use.


    If the garage is detached from the house then it doesn't matter what you do to the walls and ceiling.
    After posting that I though OSB was a better fire stop than drywall I searched the web and found the opposite. OSB will go up ln flames like a roman candle. Drywall needs to be used on common walls and ceilings, all seams and holes need to be taped.


  11. #11
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by JB Thompson View Post
    Many times (many) cars are pulled into garage only to catch fire after everyone has gone into the home.
    I'll be Rick could expound a little for us on that subject

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  12. #12
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: OSB at Garage Ceiling?

    Still another question --- if the garage wall against the conditioned area of the home were drywalled and taped, from garage floor to the roof line whereby the attic over the conditioned area was sealed off from the garage, why would some of you still be expecting the underside or the garage's roof framing to have a sealed surface?

    Sorry to be anal (something I'm quite proficient at), but I think that there has been a tendency to answer Rick's question without a full understanding of the conditions. A bad habit for any inspector.

    Eric Barker, ACI
    Lake Barrington, IL

  13. #13
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by Eric Barker View Post
    Still another question --- if the garage wall against the conditioned area of the home were drywalled and taped, from garage floor to the roof line whereby the attic over the conditioned area was sealed off from the garage, why would some of you still be expecting the underside or the garage's roof framing to have a sealed surface?

    Sorry to be anal (something I'm quite proficient at), but I think that there has been a tendency to answer Rick's question without a full understanding of the conditions. A bad habit for any inspector.

    That is the point of my question, it was not done as such.

    rick


  14. #14
    Join Date
    May 2007
    Location
    Tyler, TX
    Posts
    720

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by Eric Barker View Post
    Still another question --- if the garage wall against the conditioned area of the home were drywalled and taped, from garage floor to the roof line whereby the attic over the conditioned area was sealed off from the garage, why would some of you still be expecting the underside or the garage's roof framing to have a sealed surface?

    Sorry to be anal (something I'm quite proficient at), but I think that there has been a tendency to answer Rick's question without a full understanding of the conditions. A bad habit for any inspector.
    I re-read the original post. Not sure I'm following.

    If you are saying that the sheetrock covers the common wall of the garage and the living space (not a bedroom) and extends all of the way to the roof rafters effectively sealing off the home and there are no poke-thrus or holes. Then this is considered a firewall and is OK.

    I don't believe there is a requirement for the garage ceiling to be "sealed" if there is no common attic.

    I'll go double-check the codes.

    I know in Dallas, commerical wood construction such as a cockloft, parallel-chord trussed area between floors or attic space is supposed to be firewalled every 1000 sqft.

    Bruce Thompson, Lic. #9199
    www.TylerHomeInspector.com
    Home Inspections in the Tyler and East Texas area

  15. #15
    Join Date
    May 2007
    Location
    Tyler, TX
    Posts
    720

    Default Re: OSB at Garage Ceiling?

    Here is the separation vs. material requirement in the 2009 IRC

    R302.6 Dwelling/garage fire separation.
    The garage shall be separated as required by Table R302.6. Openings in garage walls shall comply with Section R302.5. This provision does not apply to garage walls that are perpendicular to the adjacent dwelling unit wall.

    TABLE R302.6
    DWELLING/GARAGE SEPARATION

    From the residence and attics: Not less than 1/2-inch gypsum board or equivalent applied to the garage side


    Is this what you're saying/asking? I'm fairly thick-headed and like Eric said, I'm sometimes anal. Not sure which is better.

    Bruce Thompson, Lic. #9199
    www.TylerHomeInspector.com
    Home Inspections in the Tyler and East Texas area

  16. #16
    Join Date
    Jun 2008
    Location
    Stacy, MN
    Posts
    148

    Default Re: OSB at Garage Ceiling?

    If the fire separation wall is in place between the house and the garage, then they can put up the OSB over everything else. Including the fire separation wall, covering the sheetrock.


  17. #17
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: OSB at Garage Ceiling?

    How's this for a garage ceiling! This was a drive in under the home garage at that!! I found this on an inspection yesterday.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  18. #18
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by Jim Luttrall View Post
    Must have ceiling and common walls with gypsum board for separation.
    Gypsum board is not required to be on the ceiling if this is done:
    Quote Originally Posted by chris mcintyre View Post
    Building inspector told me I could put the drywall on the wall between the house and garage all the way to the roof sheathing
    Do that and you can leave the garage ceiling open.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  19. #19
    Join Date
    May 2007
    Location
    Tyler, TX
    Posts
    720

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by Scott Patterson View Post
    How's this for a garage ceiling! This was a drive in under the home garage at that!! I found this on an inspection yesterday.
    Unfortunately, I believe it wouldn't dawn on most people until you mention it at the inspection. Then the little light comes on

    Bruce Thompson, Lic. #9199
    www.TylerHomeInspector.com
    Home Inspections in the Tyler and East Texas area

  20. #20
    Join Date
    May 2010
    Location
    St. George, UT
    Posts
    234

    Default Re: OSB at Garage Ceiling?

    I would also call out the exposed Kraft Faced insulation as being a fire hazard. It needs covered (by something with a better fire rating than plastic sheeting). Burns like gas!


  21. #21
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: OSB at Garage Ceiling?

    Quote Originally Posted by Rick Hurst View Post
    OSB at garage walls and ceilings with no gypsum board? Acceptable or not?

    Paperbacking on drywall, yes it is already noted on report.

    Opinions welcome.

    rick
    Quote Originally Posted by Larry Morrison View Post
    I would also call out the exposed Kraft Faced insulation as being a fire hazard. It needs covered (by something with a better fire rating than plastic sheeting). Burns like gas!
    .
    ....
    .
    .

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •