Results 1 to 4 of 4
  1. #1
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default thermally activated automatic vent dampers

    Anyone have an opinion (Ha,ha, that's a good one, ain't it!) on these things?

    I've think I've seem them on boilers before, but never on a water heater.

    Yes, I know it's disconnected from the draft hood. There's also a big rotted hole in the middle of the flue connector, so the whole thing got written up.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  2. #2
    Join Date
    Mar 2007
    Location
    Ridgewood, NJ
    Posts
    237

    Default Re: thermally activated automatic vent dampers

    John, I think I've read in a water heater installation manual not to re-install them. They're old and antiquated technology anyway.


  3. #3
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: thermally activated automatic vent dampers

    I don't like them and I think Neal is correct. I'd recommend that the client give it the heave-ho.

    Eric Barker, ACI
    Lake Barrington, IL

  4. #4
    Join Date
    Jul 2008
    Location
    Utah
    Posts
    390

    Default Re: thermally activated automatic vent dampers

    WOW! Although the intent may be good the risk is way too big that the thing could malfunction.

    IMO, as a father more than any other reason, I would get rid of it and deal with the minimal loss of heat as a result.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •