    Southwest US
    Default 3-2-10 rule revisited
    Does the 3 feet above the roof line only apply to wood burning fireplaces, not to gas appliances? I can't find anything in the IRC regarding this.
    Cool Re: 3-2-10 rule revisited
    chimneys
    Southwest US
    Default Re: 3-2-10 rule revisited
    Thanks Bob. Does a prefabricated gas fireplace with type B vent count as a chimney? Is it OK to have type B vents 4-6 inches above the roof line?
    Nope and nope.
    B-vent is a *vent*--not a *chimney*.
    Refer to the gas codes but they start at 12" above a flat roof then go up based upon roof pitch.
    Southwest US
    Thanks again Bob! Here is a picture of the vent I thought was too low. It's about 3 feet from the parapet and well below it but not within 3 feet of the corner. I am not sure I understand why a gas appliance would not back draft when a fireplace would? Any insight?
    You have a vertical obstruction within 8ft horizontally so the flue gas outlet must extend at least 2 feet above the top of that parapet. The 3 ft rule is to allow sparks from wood burning to cool before they land on a possibly combustible roof deck. The 2/10 is to hopefully extend the vent above any pressure zones created by wind effect over a ridge.
    The height of a vent above a roofline would have an effect on backdrafting only if it was wind related in which case it may need to extend a lot more than just the code minimum. Codes do not guarantee performance and can be exceeded.
    ... code minimum. Codes do not guarantee performance and can be exceeded.
    Expanding on what Bob said - codes are the minimum standard, with the emphasis on "MINIMUM" standard. Any 'good' builder/contractor will exceed code as code is the crappiest they are legally allowed to build.
