Results 1 to 17 of 17
Thread: PRV??
    mathew stouffer's Avatar
    mathew stouffer Guest
    Default PRV??
    I have never seen one of these before. Is this a PRV and is it adjustible.
    Default Re: PRV??
    No, does not appear to be a pressure reducing valve. Looks like this:
    Watts Brass & Tubular 3/4" Back Flo Preventer LF7U2-2 3/4
    A simple check valve.
    Ray Norton's Avatar
    Ray Norton Guest
    Default Re: PRV??
    That's a double check valve used to protect the municipal water supply. It is probably required by that particular Public/ Water Works Department/ Agency. They can also be required on sprinklered homes but judging by by what I can see of where that one is located the home is not sprinklered. It is not uncommon for those to be required to be inspected annually.
    Default Re: PRV??
    It is a "check" valve as Jim & Ray noted. Now with that little critter installed you now have a closed system and that requires an expansion tank or valve to be installed. I did not see one in the picture.
    Ray Norton's Avatar
    Ray Norton Guest
    Default Re: PRV??
    I would expect to see the expansion tank at the water heater, not at the meter, to absorb the extra pressure caused by the expansion of the heated water.
    Default Re: PRV??
    Quote Originally Posted by Ray Norton View Post
    True, for some reason I thought the WH was under the meter in that picture. I think I need to lay off the chocolate chip cookies for my afternoon snack!
    Default Re: PRV??
    "That's a double check..."
    Close.
    Thats a "Duel check valve", they are not the same as a double check.
    "It is not uncommon for those to be required to be inspected annually."
    Duel checks are not able to be tested, therefore they are not inspected.
    Double checks can be tested and are inspected annually.
    But both do serve the same purpose.
    Default Re: PRV??
    Since the code in NC now requires a backup drain pan under an expansion tank under same conditions one is required for a water heater I am seeing more expansion tanks in crawl spaces.
    Default Re: PRV??
    James is that new in the 09 irc
    Default Re: PRV??
    In NC an expansion tank is considered a hot water storage tank so the following code applies.
    504.7 Required pan. Where water heaters or hot water storage
    tanks are installed in: (a) remote locations such as a suspended
    ceiling (b) attics (c) above occupied spaces or (d) unyentilated
    craw
    I spaces the tank or water heater shall be installed in
    a galvanized steel pan having a minimum thickness of 24 gage,
    or other pans approved for such use.
    Exceptions:
    L Electric water heaters may rest in a high-impact plastic
    pan of at least lL16 inch (1 6 mill) thickness
    2. Water heater mounted on concrete floor for floor
    504.7.1 Pan size and drain. The pan shall be not less than
    1.5 inches (38 mm) deep and shall be of sufficient size and
    shape to receive all dripping or condensate from the tank or
    water heater. The pan shall be drained by an indirect waste
    pipe having a minimum diameter of 0.75 inch (19 mm). Pip- I
    ing for safety pan drains shall be of those materials listed in
    Table 605.4.
    R.A .McBride's Avatar
    R.A .McBride Guest
    Default Re: PRV??
    What code is N.C. under?
    Default Re: PRV??
    Quote Originally Posted by R.A .McBride View Post
    The 2009 NC Plumbing code is based on the 2006
    International Plumbing Code with NC amendments.
    Tom Thompson's Avatar
    Tom Thompson Guest
    Default Re: PRV??
    Scott; Installations of expansion tanks require check valves on cold inlet to heaters making the hot system closed it's self.
    Luxemburg, Wisconsin
    Default Re: PRV??
    Says right on it......... Check Valve, the technical term for a backflow preventer.
    The Bottom Line - Through an Engineer's Eyes
    Zibby Bujno's Avatar
    Zibby Bujno Guest
    Default Re: PRV??
    Its BFP (baclflow preventer) - this particular model usually is installed at closed hydronic systems (forced hot water) and water makeup line. Since its installed on main water feed for the house, make sure all water heaters have expansion tank!! Otherwise all PRVs will be leaking.
    Fuquay Varina, NC
    Default Re: PRV??
    James,
    NC amendments., can you post the verbiage because I do alot of new construction and have not yet seen a pan under the expansion tank in an attic or garage.
    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com
    Tom Thompson Guest
    Default Re: PRV??
    James,
    It's recommended by the manufacture, they do go bad. I've had several (most) fail in 2-3 years.