Results 1 to 6 of 6
  1. #1
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Heat exchanger, gas hot water boiler

    This is a 255,000 btu gas hot water boiler manufactured in 02. Looks like this was sealed after market or the guy at the factory has a bad day, too much whiskey. Anyway, do you mention this.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Heat exchanger, gas hot water boiler

    Yep, I would call for a qualified heating tech to check that over really well. There's rust stains below all that goop.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  3. #3
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Heat exchanger, gas hot water boiler

    A boiler that size could come as a package boiler or sectional boiler. I'm not too familiar with Dunkirks. Seen a few here and there but they aren't that popular here. Based on the goop I'd say it came as a sectional boiler and the guy putting it together wasn't too experienced. My old man would have beat my ass if I put a unit together like that.
    I would call it out on the basis of "Visible workmanship is very sloppy and atypical for a good boiler install; This raises concerns as to the long term integrity of the unit". OR if it did come as a package boiler. "boiler appears to have been 'resealed' for some unknown reason" recommend further blah blah
    If its been in place for ~10 years and you aren't seeing water or stains on the floor, stand or other alarms you may have a weak argument.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  4. #4
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Heat exchanger, gas hot water boiler

    Mat,

    That input should have be derated, 180,000 Btu or significantly less, you're well area is all 5,000 ft+ above sea level, isn't it?


  5. #5
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: Heat exchanger, gas hot water boiler

    Quick opinion,

    Boiler was cleaned and resealed.
    Very similar to an oil fires boiler in design.
    Would question when cleaning was done.
    I am not able to name the sealant , but if heat rated, then OK.
    If there was no sign of degradation, then OK.
    Why clean gas boiler? Increase efficiency.
    If you don't like the caulk job, well we are all not a Rembrandt.
    Better a little messy than not sealed tight.


  6. #6
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Heat exchanger, gas hot water boiler

    H.G this area is about 6700 feet.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •