Results 1 to 4 of 4
  1. #1
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Feeder cables behind bus bar in service panel

    Can the feeders be run behind the bus bar in the service disconnect. The electrical in this place was a mess so this was just par for the course, but it caught my eye. Single family home built in 01.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Feeder cables behind bus bar in service panel

    I'm going to say that is okay as I see, or think I see, a metal plate behind that panelboard interior (with the breakers) where the panelboard interior is bolted to the metal plate, and that metal plate is on standoffs, which creates that space behind the panelboard interior and the back of the enclosure.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Roger Frazee's Avatar
    Roger Frazee Guest

    Default Re: Feeder cables behind bus bar in service panel

    Quote Originally Posted by Jerry Peck View Post
    I'm going to say that is okay as I see, or think I see, a metal plate behind that panelboard interior (with the breakers) where the panelboard interior is bolted to the metal plate, and that metal plate is on standoffs, which creates that space behind the panelboard interior and the back of the enclosure.
    I would agree with Jerry. This combination enclosure is utilizing feed thru lugs to a downstream panel. I'm not sure why the green insulated ground wire is ran with the feeder.
    I see 2 hots, a neutral, and a stranded ground wire as part of the feeder cable. Then there is that insulated green wire making five wires. Where does it go?


  4. #4
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Feeder cables behind bus bar in service panel

    Ufer that i could not access


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •