    Default Double Taps Re-visited

    I know that the subject has been beaten to death, however, I don't recall this situation being discussed. I did try to look up past threads on the subject, but couldn't find any references.

    Are double taps under neutral and ground lugs allowed?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper
    Critical Home Inspection Services
    www.Home2Spec.com

  2. #2
    Join Date
    Mar 2007
    Location
    Ft. Myers, FL
    Posts
    363

    Default Re: Double Taps Re-visited

    Not neutrals, and grounds according to specs on panel.

    Paul Kondzich
    Ft. Myers, FL.

  3. #3
    Join Date
    Mar 2007
    Location
    Myrtle Beach, South Carolina
    Posts
    341

    Default Re: Double Taps Re-visited

    Would that be on All panels?

    Critical Home Inspection Services
    www.Home2Spec.com

  4. #4
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Double Taps Re-visited

    Victor,

    No. The neutrals are not supposed to be double or multi-tapped.

    Double lugged grounded conductors:
    Today’s requirements prohibit the installation of multiple grounded conductors into the same terminal for safety purposes. The NEC states the following;

    408.21"Each grounded conductor shall terminate within the panel-board in an individual terminal that is not also used for another conductor."

    Now, was this always a requirement? No. However, the reason this requirement was implemented was for safety concerns (which most electrical requirements are). One of the concerns is that an unsuspecting contractor or individual may trip a breaker thinking that he has isolated a circuit in-order to work on a given item (possibly a ceiling fan or such). Well, if the grounded conductors are double tapped under the same buss screw, the contractor who “thinks” he has isolated that circuit may very well be surprised to find out otherwise. Basically, this is a safety concern.

    Knowing what we know today, it is ill-advisable to continue to use outdated methodologies (due to safety concerns) when we now know better. If we know an item has the potential to cause a safety or overheating concern, it is our policy to always alert the client to make the necessary upgrades/ repairs.

    __________________________________________________ _______
    Below is a very good posting by James Pauley, Squre D Company:

    Log from the NEC Code Panel, regarding the new clarifying language in the Code.
    (Log #3287) 9- 113 - (384-21 (New) ): Accept

    SUBMITTER: James T. Pauley, Square D Co.

    RECOMMENDATION: Add a new 384-21 to read as follows:

    384-21. Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor. Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.

    SUBSTANTIATION: This revision is needed to coordinate the installation requirements with a long standing product standard requirement. Clause 12.3.10 of UL 67 (Panelboards) states “An individual terminal shall be provided for the connection of each branch-circuit neutral conductor.” The requirement has been enforced in the past by a close review of the manufacturers markings and by NEC 110-3(b). However, since it is a rule that specifically effects how the installer can make connections, it is important that it be in the NEC. Even with the manufacturers markings, inspectors still indicate that they see a number of panelboards installed with two (or more) branch circuit neutrals under one terminal or they see an equipment grounding conductor and neutral under the same terminal.

    There is very good rationale for the requirement in the product standards. Doubling up on the neutrals creates a significant problem when the circuit needs to be isolated. In order to isolate the circuit, the branch breaker is turned off and the neutral is disconnected by removing it from the terminal. If the terminal is shared with another circuit, the connection on the other (still energized) circuit will be loosened as well. This can wreak havoc, particularly if the neutral is part of a 120/240V multi-wire branch circuit. Also, the neutral assemblies are not evaluated with doubled-up neutrals in the terminals.

    The connection of a neutral and equipment grounding conductor creates a similar issue. One of the objectives of the particular arrangement of bonding jumpers, neutrals and equipment grounds is to allow circuit isolation while keeping the equipment grounding conductor still connected to the grounding electrode (see UL 896A - Reference standard for Service Equipment). When the neutral is disconnected, the objective is to still have the equipment ground solidly connected to the grounding electrode. If both the neutral and grounding conductor are under the same terminal, this cannot be accomplished.

    This addition to the NEC does not change any product or permitted wiring arrangement from what it is today. It will however, it will help installers to avoid wiring the panel in violation of 110- 3(b) and then have to contend with a red-tag from the inspector. The code language is proposed in a fashion to allow consistent enforcement of the provision by the AHJ. Although the UL wording is adequate for the product standard, it is important that the NEC language is as clear an unambiguous as possible. This is the reason for specifically noting that the terminal cannot be used for another conductor.

    Furthermore, the code requirement has been worded to make sure that both branch circuit and feeder neutrals are covered since it is not uncommon to have feeder breakers as well as branch breakers in the panel-board (the issue for the neutral is the same regardless of branch or feeder).

    Also, the term “grounded conductor” is used to be consistent with the code terminology and to recognize that not all grounded conductors are neutrals. An exception has been proposed to avoid any confusion relative to parallel circuit arrangements. In these instances, multiple neutrals could be in a single terminal if the terminal has been identified as acceptable for multiple conductors.

    PANEL ACTION: Accept.
    NUMBER OF PANEL MEMBERS ELIGIBLE TO VOTE: 11
    VOTE ON PANEL ACTION:
    AFFIRMATIVE: 11

    ______________________________________


  5. #5
    Join Date
    Mar 2007
    Location
    Myrtle Beach, South Carolina
    Posts
    341

    Default Re: Double Taps Re-visited

    Thank you.

    Critical Home Inspection Services
    www.Home2Spec.com

  6. #6
    Join Date
    Mar 2007
    Location
    Mount Pleasant, SC
    Posts
    100

    Default Re: Double Taps Re-visited

    Old thread bump - Jerry, is this still the reference for this common call out. My clients got this today from the local AHJ...

    "After inspecting the panel at 2xxx River Bluff Ln. and reviewing the National Electrical Code. I found no code sections that restrict two neutrals in one lug.

    Sean Kxxxx
    Town of xxxx
    Building Inspector"


    ??????????????????????????????????????????????

    We know why you fly: because the bus is too expensive and the railroad has a dress code...
    www.atozinspector.com

  7. #7
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Double Taps Re-visited

    Quote Originally Posted by Mike Gault View Post
    Old thread bump - Jerry, is this still the reference for this common call out. My clients got this today from the local AHJ...

    "After inspecting the panel at 2xxx River Bluff Ln. and reviewing the National Electrical Code. I found no code sections that restrict two neutrals in one lug.

    Sean Kxxxx
    Town of xxxx
    Building Inspector"


    ??????????????????????????????????????????????
    WOW!!! That was from an AHJ????

    2008 NEC:

    408.41 Grounded Conductor Terminations.
    Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.



  8. #8
    Join Date
    Mar 2007
    Location
    Mount Pleasant, SC
    Posts
    100

    Default Re: Double Taps Re-visited

    Yeah, and I'm trying to figure out how to respond without being condescending (and it's quite difficult) to him.

    We know why you fly: because the bus is too expensive and the railroad has a dress code...
    www.atozinspector.com

  9. #9
    Join Date
    Mar 2007
    Location
    Mount Pleasant, SC
    Posts
    100

    Default Re: Double Taps Re-visited

    It's was also 408.11 at some point back, was it not? Home is about 4 years old...

    We know why you fly: because the bus is too expensive and the railroad has a dress code...
    www.atozinspector.com

  10. #10
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Double Taps Re-visited

    Quote Originally Posted by Mike Gault View Post
    Yeah, and I'm trying to figure out how to respond without being condescending (and it's quite difficult) to him.
    I know what that can be like.

    I know you guys don't like to do code, but just politely suggest to him that he read that code section. If he refuses it is out of your hands I would think.


  11. #11
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Double Taps Re-visited

    I have:
    2002 NEC - 408.21
    2005 NEC - 408.41


  12. #12
    Join Date
    Mar 2007
    Location
    Mount Pleasant, SC
    Posts
    100

    Default Re: Double Taps Re-visited

    Thanks Petey... you rock.

    And yes, I'll be polite, even in the email. :-)

    We know why you fly: because the bus is too expensive and the railroad has a dress code...
    www.atozinspector.com

  13. #13
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Double Taps Re-visited

    Keep in mind, 384.21 never made it into the 1999 NEC, so prior to 2002 this was NOT an NEC code requirement, other than that of the manufacturer's listing and instructions.


  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Double Taps Re-visited

    Quote Originally Posted by Speedy Petey View Post
    Keep in mind, 384.21 never made it into the 1999 NEC, so prior to 2002 this was NOT an NEC code requirement, other than that of the manufacturer's listing and instructions.
    Which means it was a violation of 110.3(B) in the NEC.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Join Date
    Mar 2007
    Location
    Mount Pleasant, SC
    Posts
    100

    Talking Re: Double Taps Re-visited

    Knew you'd be here Jerry... thanks

    We know why you fly: because the bus is too expensive and the railroad has a dress code...
    www.atozinspector.com

  16. #16
    Join Date
    May 2008
    Location
    Atlanta
    Posts
    120

    Default Re: Double Taps Re-visited

    Quote Originally Posted by Richard Rushing View Post
    Well, if the grounded conductors are double tapped under the same buss screw, the contractor who “thinks” he has isolated that circuit may very well be surprised to find out otherwise. Basically, this is a safety concern.
    Richard,

    Trying to understand this. I'm not seeing how a double tapped ground is any less isolated than 2 grounds under their own lug (which would then be connected to the same buss).


  17. #17
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Double Taps Re-visited

    Quote Originally Posted by Brent Crouse View Post
    Richard,

    Trying to understand this. I'm not seeing how a double tapped ground is any less isolated than 2 grounds under their own lug (which would then be connected to the same buss).
    Brent,

    Go back and read the entire section, including the sentences before the one you are questioning.

    This is an excellent example of why taking something out of context loses what is being said and allow you to think it is saying something else.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  18. #18
    Join Date
    May 2008
    Location
    Atlanta
    Posts
    120

    Default Re: Double Taps Re-visited

    Nope, I'm still not seeing it. Is this implying that by having doubled tapped neutrals, it becomes more likely for current from the other circuit to "backflow" up the other neutral, and thus become a shock hazard to the "isolated" circuit?


  19. #19
    Join Date
    Mar 2007
    Location
    Mount Pleasant, SC
    Posts
    100

    Default Re: Double Taps Re-visited

    Back from my meeting at Town Hall with Sean.

    They are allowing it via an exception in the 2003 IRC (enforced during the build in 2005) from section 3606.4 with the exact same exception verbiage from the 384.21 proposal language.

    "Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor."

    I lost (evidently)... even though I explained how others enforce it (other counties and municipalities) He will re address it at next Tuesdays Building officials meeting...

    p.s. Home Buyer is having them separated immediately after closing.

    p.p.s Sad thing is there was always room there to have done it correctly to start with...

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    We know why you fly: because the bus is too expensive and the railroad has a dress code...
    www.atozinspector.com

  20. #20
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Double Taps Re-visited

    (red and underlining is mine for highlighting)
    Quote Originally Posted by Richard Rushing View Post
    One of the concerns is that an unsuspecting contractor or individual may trip a breaker thinking that he has isolated a circuit in-order to work on a given item (possibly a ceiling fan or such). Well, if the grounded conductors are double tapped under the same buss screw, the contractor who “thinks” he has isolated that circuit may very well be surprised to find out otherwise. Basically, this is a safety concern.

    Quote Originally Posted by Brent Crouse View Post
    Nope, I'm still not seeing it. Is this implying that by having doubled tapped neutrals, it becomes more likely for current from the other circuit to "backflow" up the other neutral, and thus become a shock hazard to the "isolated" circuit?
    .Yes.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  21. #21
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Double Taps Re-visited

    Quote Originally Posted by Mike Gault View Post
    Back from my meeting at Town Hall with Sean.

    They are allowing it via an exception in the 2003 IRC (enforced during the build in 2005) from section 3606.4 with the exact same exception verbiage from the 384.21 proposal language.

    "Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor."

    I lost (evidently)... even though I explained how others enforce it (other counties and municipalities) He will re address it at next Tuesdays Building officials meeting...
    Mike,

    Take this section from the 2003 IRC with you and meet with him again. I'm betting he changes his mind.
    (red text is mine)
    - E3306.6 Conductors in parallel. Circuit conductors that are electrically joined at each end to form a single conductor shall be limited to sizes No. 1/0 and larger. Conductors in parallel shall be of the same length, same conductor material, same circular mil area and same insulation type. Conductors in parallel shall be terminated in the same manner. Where run in separate raceways or cables, the raceway or cables shall have the same physical characteristics.

    Ask him: 1) are those conductors 1/0 and larger?; 2) are those conductors of the same length?

    "Conductors in parallel" has a completely different meaning that what he applied.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  22. #22
    James Foy's Avatar
    James Foy Guest

    Default Re: Double Taps Re-visited

    Quote Originally Posted by Richard Rushing View Post
    Victor,

    ...
    Now, was this always a requirement? No. However, the reason this requirement was implemented was for safety concerns (which most electrical requirements are). One of the concerns is that an unsuspecting contractor or individual may trip a breaker thinking that he has isolated a circuit in-order to work on a given item (possibly a ceiling fan or such). Well, if the grounded conductors are double tapped under the same buss screw, the contractor who “thinks” he has isolated that circuit may very well be surprised to find out otherwise. Basically, this is a safety concern.
    ...
    Also, the term “grounded conductor” is used to be consistent with the code terminology and to recognize that not all grounded conductors are neutrals. An exception has been proposed to avoid any confusion relative to parallel circuit arrangements. In these instances, multiple neutrals could be in a single terminal if the terminal has been identified as acceptable for multiple conductors.

    ______________________________________
    Thanks for the reference. Always enforced it, but hadn't thought about the back current flowing around via a untripped breaker. Now I know why.


  23. #23
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Re: Double Taps Re-visited

    I'm missing something here.

    Quite ofter we see wire nuts used to connect both ground and neutral connections in multiple branch circuits, in Service equipment panels and in J-boxes throughout the home. Many of these are not the same circuit, but a common connection of multiple neutrals and grounds that are daisy chained within these wire nut connections.

    Why is it not OK at the service equipment panel terminal bar, but OK within the branch circuit wiring???


  24. #24
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Double Taps Re-visited

    Grounding conductors from multiple circuits should be connected together. Neutrals from different circuits should not be connected unless you are dealing with a multiwire branch circuit. To do so otherwise could potentially overload the neutral.

    It is not ok in the panel since there is a code prohibition against it.


  25. #25
    Join Date
    Apr 2008
    Location
    Western Massachusetts
    Posts
    536

    Default Re: Double Taps Re-visited

    While I agree that it is prohibited in code, the 'why' described here is unfortunately wrong.

    Double-tapped neutrals place two neutral conductors in the same terminal on a bus bar. Single-tapped neutrals separate those two neutral conductors on the bus bar by... a conductor! That means when those single-tapped or double-tapped neutrals are in the bus bar, there is NO difference between them in terms of conductivity. Therefore simply tripping the breaker does NOT isolate the circuit. You can only isolate circuits by disconnecting ALL conductors from shared busses. A standard breaker only disconnects 1 of the 3+ conductors.

    The difference, and potential danger, is when the neutrals are double-tapped and somehow become isolated from the neutral bus bar. In that case, the current flow travels from the hot wire, through the load, along the neutral wire, jumps to the other neutral wire, and up to the supposedly disconnected load. This is the only scenario in which a double-tapped neutral might be more problematic (from a shock hazard point of view) than single-tapped - assuming the equipment supports both.

    Therefore the logical remedy would be to only allow double-tapped neutrals if the equipment manufacturer states the terminal is designed to support such an installation. This also addresses the potential arcing problems and such when installed according to manufacturer directions. The NEC takes it one step further than this minimum safety requirements and disallows double-tapped neutrals altogether.


  26. #26
    Join Date
    Dec 2007
    Location
    Holladay, UT
    Posts
    577

    Default Re: Double Taps Re-visited

    Tom Rees / A Closer Look Home Inspection / Salt Lake City, Utah
    http://acloserlookslc.com/

  27. #27
    Join Date
    Mar 2007
    Location
    Mount Pleasant, SC
    Posts
    100

    Default Re: Double Taps Re-visited

    Quote Originally Posted by Jerry Peck View Post
    Mike,

    Take this section from the 2003 IRC with you and meet with him again. I'm betting he changes his mind.
    (red text is mine)
    - E3306.6 Conductors in parallel. Circuit conductors that are electrically joined at each end to form a single conductor shall be limited to sizes No. 1/0 and larger. Conductors in parallel shall be of the same length, same conductor material, same circular mil area and same insulation type. Conductors in parallel shall be terminated in the same manner. Where run in separate raceways or cables, the raceway or cables shall have the same physical characteristics.

    Ask him: 1) are those conductors 1/0 and larger?; 2) are those conductors of the same length?

    "Conductors in parallel" has a completely different meaning that what he applied.
    I give him this and let you know the outcome of Tuesdays meeting...

    Thanks...