    Default boiler installed in garage space - sort of

    I inspected a home today and the boiler was installed in the back of a garage but has been enclosed in a utility room - does the ignition source need to be 18" off the floor - the utility room does not share any open space with the garage and the door is not vented. I am in westchester county, NY. Thank

    Similar Threads:
    Member Benefits1

  2. #2
    Tom Thompson's Avatar
    Tom Thompson Guest

    Default Re: boiler installed in garage space - sort of

    18" not required as described, the room is separate and not part of the garage, if it was drawing combustion air from the garage 18" rule must be followed.


  3. #3
    Join Date
    Mar 2011
    Location
    Croton on Hudson NY
    Posts
    6

    Default Re: boiler installed in garage space - sort of

    Thats what I thought, but wanted to be sure - thanks for the quick reply Tom


  4. #4
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: boiler installed in garage space - sort of

    Quote Originally Posted by Tom Thompson View Post
    ... if it was drawing combustion air from the garage 18" rule must be followed.
    Which begs the question, where is the combustion air coming from? Is the utility room really big enough to provide it, or is there some other source?

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)