    Default Attic insulation

    House I was in today, under construction, the upstairs rooms are built into the attic ( attic space above and on the other side of at least one wall).
    Questions are:
    What is the insulation requirement for the wall?
    Also the same wall has a pressed wood hollow core door going into the attic, should this be an insulated door instead of hollow?

    Thanks

    PS; My IRC is at the office, I'm not.

    Similar Threads:
    Crawl Space Creeper
    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Attic insulation

    Quote Originally Posted by Rick Cantrell View Post
    Questions are:
    What is the insulation requirement for the wall?
    Same as for the attic ceiling.

    Also the same wall has a pressed wood hollow core door going into the attic, should this be an insulated door instead of hollow?
    In *MY* opinion, "Yes.", but we went through a biggie discussion on this recently and I think it was split half and half for the insulated door.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Attic insulation

    Thanks JP,
    I thought it should be the same requirement as the ceiling insulation, and I don't think to much of the hollow cord doors either.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  4. #4
    Join Date
    Apr 2007
    Location
    state of jefferson
    Posts
    522

    Default Re: Attic insulation

    walls do not require same r value as ceiling.the requirements are usually found in the energy calcs or prescriptive code requirements for your area. here we require r-38 for ceilings and r-21 for walls to meet a prescriptive approach. skylight shafts extending thru attics get wrapped with wall r-value insulation. i suppose it could differ for your area so ask for the approved plans or ask the inspector what is required


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Attic insulation

    Quote Originally Posted by brian schmitt View Post
    walls do not require same r value as ceiling.
    Quite incorrect when relating that answer to the question posted:

    (what was stated)
    the upstairs rooms are built into the attic ( attic space above and on the other side of at least one wall)

    (the question)
    Questions are:
    What is the insulation requirement for the wall?

    For walls WHICH HAVE ATTIC on the other side, the walls are required to be insulated to the same as the *ceiling to the attic*.

    If R-30 is required for the attic/ceiling, then R-30 is also required for the attic/walls.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Attic insulation

    Jerry, do you have a code reference on that?
    Jim

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Attic insulation

    Yes.

    (from the Florida Building Code)

    The same logic applies to thermal envelopes around the world, though.

    13-604.1.A.1 Walls considered ceiling area.
    Wall areas that separate conditioned living space from unconditioned attic space (such as attic knee walls, walls on cathedral ceilings, skylight chimney shafts, gambrel roofs, etc.) shall be considered ceiling area. Such areas shall be included in calculations of ceiling area and shall have a minimum insulation value of R-19.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Attic insulation

    I agree that logic dictates that walls in an attic have the same thermal load as a ceiling and the standard R-11 wall is wrong, logically. I was hoping there was something that I had missed in the energy code or IRC that might address it. It is mighty tough to get a vertical wall up to R-38 or R-49 though. I have added more for knee walls on personal homes, but then I did lots of things above code.
    Jim

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    Join Date
    Apr 2007
    Location
    state of jefferson
    Posts
    522

    Default Re: Attic insulation

    jerry,
    a wall has different heat lost due to it being 60 degrees or greater from a horizontal plane(definition per u.b.c.). the greater r-value for ceilings are due to heat rising to a horizontal plane. a wall does not require the same r-value here as you mentioned in florida code. it seems like an exception to the norm but i get the feeling that you can be that also . i have little exposure to oher parts of the country and their energy code requirements pertaining to this issue but it would be interesting to know the why and wheres.


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Attic insulation

    Quote Originally Posted by brian schmitt View Post
    but it would be interesting to know the why and wheres.
    From what I read and was told years ago, it's because:

    1) 'exterior' walls are applicable as you described, albeit to the outdoor temperature

    2) 'attic ceilings' are applicable as you described, *and*, the attic ceiling is exposed to the much higher temperatures of the attic, not 'the outdoor' temperature

    3) 'attic walls treated as ceiling area' a combination of 1) and 2), being, as you described, 'not a horizontal plane' but also being exposed to 'the higher temperatures of the attic', thus requiring additional insulation over and above the requirements of the 'exterior' walls

    Now, do the 'attic walls treated as ceiling area' require the full insulation of the 'attic ceiling' to attain the same thermal envelope effectiveness as the 'attic ceiling', beats the heck out of me ... but I can tell you that 'attic walls treated as ceiling area' absolutely do require more insulation than 'exterior' walls to attain the same thermal envelope provided by the 'attic ceiling' insulation and that provided by the 'exterior' wall insulation.

    Would some 'in between' R value provide the same effective thermal envelope? Maybe, but 'eyes ain't smart 'nough to figger dat out'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Attic insulation

    Here is an interesting document that I came across.

    http://www.homeenergy.org/archive/hem.dis.anl.gov/eehem/93/930104.html

    It talks about the loss of effective R value in cold temperatures.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Attic insulation

    Jim,

    Interesting information, I noticed that was from 15 years ago - wonder what changes were made to loose fill and when?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com