    Feb 2011
    Ohio
    Default Max bends of a furnace flue
    Does anyone know code or rules or the amount of bends allowed on a flue?
    A HWT and a 92,000 BTU furnace flue connect together properly, (single wall pipe) but then have 3, 90 degree bents, each about 3" apart before they
    turn up into a "B" vent pipe. (a total of 4 bends including the turn up, from the furnace and up, at the end of the run, into the B pipe) All piping slopes up properly, about an inch per foot.
    Thanks / Richard
    Default Re: Max bends of a furnace flue
    I remember reading about a max # of bends rule when I was training years ago but have since learned that it all pretty much comes down to manufacturer specs. There are tables and rules in the extensive fuel/gas code but in most cases the manf. instructions are your best bet.
    What you describe sounds odd..... a picture would help a bunch.
    Tom Thompson's Avatar
    Tom Thompson Guest
    CA. code
    Only 1/3rd of the total vertical vent rise can be horizontal, any angel greater than 45 degrees is considered horizontal. No more that one offset not greater than 60 degrees is allowed. 75% of the total vent must be vertical. The vent connector (between appliance and chimney) can be installed at 1/4" per foot rise, it's still figured into the 1/3 rd horizontal.
