    Anyone know about how much air space is necessary in front of a typical waste vent or otherwise before it becomes an issue.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Vent caps

    Marc,

    Seems to me that it would be necessary to calculate the area of the pipe opening and compare it to the area of the opening at that slot between the top of the vent pipe and the underside of the cap to see if they match. If the slot is less, then it would probably need correction.

    Assuming my math is correct...

    The area of an 1 1/2" pipe cross section is approximately 1.8 sq.in.
    The area of a 2" pipe cross section is approximately 3.1 sq.in.

    The circumference of an 1 1/2" pipe is approximately 4.7"
    The circumference of a 2" pipe is approximately 6.2"

    So, in order for you to get 1.8 sq.in. on a 1 1/2" pipe, you would need a gap/slot that was approximately 3/8" and about 1/2" on the 2" pipe.

    If my REALLY rusty math is correct.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  3. #3
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Vent caps

    Quote Originally Posted by Gunnar Alquist View Post
    Marc,

    Seems to me that it would be necessary to calculate the area of the pipe opening and compare it to the area of the opening at that slot between the top of the vent pipe and the underside of the cap to see if they match. If the slot is less, then it would probably need correction.

    Assuming my math is correct...

    The area of an 1 1/2" pipe cross section is approximately 1.8 sq.in.
    The area of a 2" pipe cross section is approximately 3.1 sq.in.

    The circumference of an 1 1/2" pipe is approximately 4.7"
    The circumference of a 2" pipe is approximately 6.2"

    So, in order for you to get 1.8 sq.in. on a 1 1/2" pipe, you would need a gap/slot that was approximately 3/8" and about 1/2" on the 2" pipe.

    If my REALLY rusty math is correct.
    oooooo I get it. Actually, I thought there was more to it. I was "overthinking" it. A+ buddy..


  4. #4
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Vent caps

    Since when does a sewer vent need a cap?

    #1 looks like you could just reef up on it and gain an inch or so. I don't get #2.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  5. #5
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Vent caps

    Quote Originally Posted by John Kogel View Post
    Since when does a sewer vent need a cap?

    #1 looks like you could just reef up on it and gain an inch or so. I don't get #2.
    I didnt think they do but as long as they were there; just wanted to verify they received enough air volume.


  6. #6
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Question Re: Vent caps

    Did they run DWV pipe inside of an upside-down B-vent in pic#2?

    Keep the fire in the fireplace.

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Vent caps

    Quote Originally Posted by Marc M View Post
    Anyone know about how much air space is necessary in front of a typical waste vent or otherwise before it becomes an issue.

    "typical waste vent "

    If that is a plumbing vent, the tops need to be removed and the top of the vent open to the outdoor air.

    There is no reason to even consider installing a cap over a plumbing vent - it already has water in it ... it is made to get wet and have water in it.

    Is that first photo a photo of broken off PVC?

    The second photo, is that PVC in that B vent (as Bob asked)? If so, that is the completely wrong use and completely wrong flashing for the plumbing vent, and the completely wrong ... everything ...