    Default Ground Rod @ meter base

    Inspected this house today, built in the early 80's. This house had the ground rod at meter base up by the rod about 100 yards from the from of the house. The main wire went underground about 120 yards to the the panel, with no ground at the main panel just the 1 at the road. Is this acceptable???

    Similar Threads:
    Last edited by Sam Morris; 07-30-2011 at 06:32 AM. Reason: Ground Rod
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Orlando, FL
    Posts
    1,592

    Default Re: Ground round @ meter base

    Do you have a photo of this setup and one of inside of the panel?


  3. #3
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Ground round @ meter base

    Are you refering to a manufactured home connection from a pedestal?

    Are you suggesting there was no bonding at the equipment?

    There should be more than one conductor ("wire") from the equipment. How many conductors are present? Is there a main disconnect at this "meter" location? Protection? (main power feeder, service lateral, etc.).

    Was there any other metalic or return path between these two structures?

    Are you aware that there are more than one type of electrode ("made" or otherwise), i.e. there are other options besides "rods" which can be used in a grounding electrode system.


  4. #4
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Re: Ground round @ meter base

    Quote Originally Posted by H.G. Watson, Sr. View Post
    Are you refering to a manufactured home connection from a pedestal?

    Are you suggesting there was no bonding at the equipment?

    There should be more than one conductor ("wire") from the equipment. How many conductors are present? Is there a main disconnect at this "meter" location? Protection? (main power feeder, service lateral, etc.).

    Was there any other metallic or return path between these two structures?

    Are you aware that there are more than one type of electrode ("made" or otherwise), i.e. there are other options besides "rods" which can be used in a grounding electrode system.
    The equipment was bonded to the panel, but there was no ground (rod or plumbing) at the panel only at the meter (no main disconnect at meter) 5000 sq ft house. Don't know of a return path.. Thanks

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  5. #5
    Join Date
    Mar 2007
    Location
    Atlanta, Georgia
    Posts
    1,088

    Default Re: Ground round @ meter base

    There are double taps on the top two breakers. There are neturals that cross over the panel just above the top breakers. That is a target rich environment. Sparky needs to come out and fix lots of stuff. Have him fix any missing ground at the same time.