Results 1 to 4 of 4
  1. #1
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Not sure what to make of this junction box

    Member Benefits1
    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  2. #2
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Not sure what to make of this junction box

    It doesn't need a cover, but it needs a cable clamp.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  3. #3
    Roger Frazee's Avatar
    Roger Frazee Guest

    Default Re: Not sure what to make of this junction box

    Quote Originally Posted by John Arnold View Post
    There ain't no junction!
    Congratulations you have found another mystery box. It's really speculation at this point, but apparently the person who did this was thinking that he may make a splice in that metal box. There are several issues that I see in the photo but none that I would lose sleep over unless those individual conductors that are wire tied are carrying line voltage, that is a big no no. The good news is the jb does appear that it will remain accessible even if a splice is made.


  4. #4
    Join Date
    Mar 2011
    Location
    Virginia Beach, VA
    Posts
    123

    Default Re: Not sure what to make of this junction box

    John,

    There are three big concerns that I have.

    1) There is no bushing/clamp protecting the cables going into or out of the JB on the right side. The wires may well fray or be cut.

    2) The left side of the JB shows the Gray cable exiting the from the top of the JB.

    3) There is no cover for the JB. And if there was one, it would crush the gray wire.

    Personal opinion, "Here comes the Red Tag".