Results 1 to 7 of 7
  1. #1
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Townhouse - self closing garage doors

    Do doors that lead from a garage (all garages connected together) to a common area have to be self closing?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    James Foy's Avatar
    James Foy Guest

    Default Re: Townhouse - self closing garage doors

    If the corridor they join is habitable (has ducting going to it) then they all need to be self closing to prevent the fast spreading of fire, smoke, and poisonous gases. If the corridor has one hour fire resistance, than the door from the corridor to the other habitable portions of the building needs to be self closing.


  3. #3

    Default Re: Townhouse - self closing garage doors

    Quote Originally Posted by Marc M View Post
    Do doors that lead from a garage (all garages connected together) to a common area have to be self closing?
    From the picture, this appears to be a common hallway. This is usually considered a one-hour "fire corridor" for safe exit. All doors usually are required to be self closing fire rated doors to prevent spread of fire. You often see them held open by magnetic catches tied to the fire alarm system if there is one.
    You also often see fire doors to stairwells and such blocked open by residents. This is a huge fire code violation that I frequently call out.

    True Professionals, Inc. Property Consultant
    877-466-8504

  4. #4
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Townhouse - self closing garage doors

    Quote Originally Posted by Dana Bostick View Post
    From the picture, this appears to be a common hallway. This is usually considered a one-hour "fire corridor" for safe exit. All doors usually are required to be self closing fire rated doors to prevent spread of fire. You often see them held open by magnetic catches tied to the fire alarm system if there is one.
    You also often see fire doors to stairwells and such blocked open by residents. This is a huge fire code violation that I frequently call out.
    that's kinda what I figured..


  5. #5
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Townhouse - self closing garage doors

    No.

    What your describing would not be a "townhouse" under the IRC, or california's current version of same - but fall under the former CBC version of the UBC or IBC.

    I suspect the inspected was and is actually a Condo and you have photographed limited common and shared limited common elements.

    I further suspect and that none of the units themselves share the separation with that of the garage(s) spaces and are further separated by common or limited common hall/foyer/ space and that the doors to the actual habital units have self-closing doors with thresholds. There is likely a non-locking door separating this "garage"/storage "hall" from the entrance foyer/common egress/exit path from the units which opens to that foyer (escape path FROM the common garage hall) has a closer and may or may not be held open with electro magnet integrated with fire detection system. The deadbolts on those garage exit doors should not require a key to operate from inside the garage space(s) and the partition walls between the garage spaces themselves are likely NOT separation walls.

    Last edited by H.G. Watson, Sr.; 08-29-2011 at 08:09 AM.

  6. #6
    Sandie Hastings's Avatar
    Sandie Hastings Guest

    Default Re: Townhouse - self closing garage doors

    They are fire doors and they need to self-close and latch. (IFC 703.2.3)


  7. #7
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Townhouse - self closing garage doors

    Quote Originally Posted by H.G. Watson, Sr. View Post
    No.

    What your describing would not be a "townhouse" under the IRC, or california's current version of same - but fall under the former CBC version of the UBC or IBC.

    I suspect the inspected was and is actually a Condo and you have photographed limited common and shared limited common elements.

    I further suspect and that none of the units themselves share the separation with that of the garage(s) spaces and are further separated by common or limited common hall/foyer/ space and that the doors to the actual habital units have self-closing doors with thresholds. There is likely a non-locking door separating this "garage"/storage "hall" from the entrance foyer/common egress/exit path from the units which opens to that foyer (escape path FROM the common garage hall) has a closer and may or may not be held open with electro magnet integrated with fire detection system. The deadbolts on those garage exit doors should not require a key to operate from inside the garage space(s) and the partition walls between the garage spaces themselves are likely NOT separation walls.
    Wow, impressive. You're correct in that they are condos. My mistake calling them townhouses.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •